Hello All,

I tend to use these for these situations  8.17.2.4.4 is the key to them.

8.17.2.4.2   For single systems, the fire department connection shall be 
installed  as follows:

(1)  Wet system — on the system side of system control, check, and alarm valves 
(see Figure A.8.16.1.1)
(2)  Dry system — between  the  system control valve and  the dry pipe valve
(3)  Preaction system — between  the preaction valve and the check valve on the 
system side of the preaction valve
(4)  Deluge system — on the system side of the deluge  valve

8.17.2.4.3   For multiple systems, the fire department connection shall be 
connected between 
the supply control valves and the system control valves.

8.17.2.4.4* The requirements of 8.17.2.4.2 and 8.17.2.4.3 shall not apply where 
the fire department 
connection is connected to the underground piping.






-- 
Best regards,
 Charles                            mailto:[email protected]