I still have the check valve from a Ames that failed to open. 
It was jammed shut, discovered when I was called out because they couldn't do 
the fire pump test. 

In another case, I tested a backflow and it failed (on a Best Buy store). I 
opened the valve up and the check was damaged, would only open a third. 



Sent from my iPhone

On Jul 24, 2013, at 8:53 PM, Ron Greenman <[email protected]> wrote:

> Worked well for plumbing and process piping applications as they are
> constantly being exercised.
> 
> 
> On Wed, Jul 24, 2013 at 5:12 PM, Dwight Havens <[email protected]>wrote:
> 
>> I do remember the ones with the rods in the center of the valve being
>> particularly poor.
>> 
>> Dwight
>> 
>> 
>> 
>> 
>> ________________________________
>> From: Ron Greenman <[email protected]>
>> To: [email protected]
>> Sent: Tuesday, July 23, 2013 11:25 PM
>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>> 
>> 
>> By the mid-nineties you have the early Ames models purpose built for
>> sprinklers readily available, but many units being installed are still not
>> listed for fire service as many jurisdictions don't consider the fire line
>> a fire line until after the backflow, and a n on-listed device is cheaper
>> than a listed one. Plus many go back to the seventies and many used weights
>> instead of springs and complicated lever systems for joining the clappers
>> and weights. Wish I could post a picture.
>> 
>> 
>> On Tue, Jul 23, 2013 at 7:33 PM, Dwight Havens <[email protected]
>>> wrote:
>> 
>>> Give me a time frame. My best recollection is the mid '90's.
>>> 
>>> Dwight
>>> 
>>> 
>>> 
>>> 
>>> ________________________________
>>> From: Ron Greenman <[email protected]>
>>> To: [email protected]
>>> Sent: Tuesday, July 23, 2013 9:12 PM
>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>>> 
>>> 
>>> Were these the plumbing type before fire service listed devices existed.
>>> 
>>> 
>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight Havens <[email protected]
>>>> wrote:
>>> 
>>>> Yes, yes, and yes.  The original proposal was based on observed
>> failures
>>>> of BFPAs to operate properly during main drain testing.
>>>> 
>>>> Glendale, AZ public library specifically comes to mind.
>>>> 
>>>> Dwight
>>>> 
>>>> 
>>>> 
>>>> 
>>>> ________________________________
>>>> From: Todd Williams <[email protected]>
>>>> To: "[email protected]" <
>>>> [email protected]>
>>>> Sent: Monday, July 22, 2013 9:32 PM
>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>>>> 
>>>> 
>>>> Has there ever been an instance of system failure due to the backflow
>> not
>>>> properly opening? How about detection of a BFP problem during a full
>> flow
>>>> test. How about something subsequent to the initial acceptance?
>>>> 
>>>> Todd G Williams, PE
>>>> Fire Protection Design/Consulting
>>>> Stonington, CT
>>>> 860-535-2080
>>>> www.fpdc.com
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> 
>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> 
>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> 
>>> 
>>> 
>>> 
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> [email protected]
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon,
>>> essayist, philosopher, and statesman (1561-1626)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>> 
>> 
>> 
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis Bacon,
>> essayist, philosopher, and statesman (1561-1626)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to