No. 
The intent is not to pitot the output but to exercise the valve. 

Sent from my iPhone

On Jul 25, 2013, at 10:56 AM, Ron Greenman <[email protected]> wrote:

> Forest. What were you flowing to discover these failures? Main drain or
> some special test header? Would a sign with the data requested by the
> customer that started this thread have had any utility in helping you
> discover the problem?
> 
> Then back to that perennial question of what's a "full flow " test and how
> do you do one? I think Roland said the intent was to flow an equivalent to
> the design discharge criteria. How do you do this? Do we run a pitot
> somewhere on the system? Do we catch and measure discharge? If so, from
> where? How do we arrange the test port(s)? Do we flow the design area or
> simulate it elsewhere? Do we need results of at least or better flow or
> right on the money flow? If not either of those how do we judge?
> 
> Doesn't the hydraulic data plate note the required psi per the calcs at the
> BOR and the static? Isn't the difference the residual drop at that point
> relative to the design area? Wouldn't a main drain with good flow at a psi
> around the BOR rating, and returning to close to the noted static when
> terminated suggest a fully open valve, or an adequately open valve if the
> UG is oversized? In the latter case the partially open valve is equivalent
> to fully open for the system I just described. Am I missing something here?
> An erroneous a priori? My understanding of hydraulics wrong? Main drains
> are too small to simulate the result of all design area heads flowing as
> the water passes through the BOR?
> 
> 
> On Thu, Jul 25, 2013 at 7:34 AM, Forest Wilson <[email protected]>wrote:
> 
>> I still have the check valve from a Ames that failed to open.
>> It was jammed shut, discovered when I was called out because they couldn't
>> do the fire pump test.
>> 
>> In another case, I tested a backflow and it failed (on a Best Buy store).
>> I opened the valve up and the check was damaged, would only open a third.
>> 
>> 
>> 
>> Sent from my iPhone
>> 
>> On Jul 24, 2013, at 8:53 PM, Ron Greenman <[email protected]> wrote:
>> 
>>> Worked well for plumbing and process piping applications as they are
>>> constantly being exercised.
>>> 
>>> 
>>> On Wed, Jul 24, 2013 at 5:12 PM, Dwight Havens <[email protected]
>>> wrote:
>>> 
>>>> I do remember the ones with the rods in the center of the valve being
>>>> particularly poor.
>>>> 
>>>> Dwight
>>>> 
>>>> 
>>>> 
>>>> 
>>>> ________________________________
>>>> From: Ron Greenman <[email protected]>
>>>> To: [email protected]
>>>> Sent: Tuesday, July 23, 2013 11:25 PM
>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>>>> 
>>>> 
>>>> By the mid-nineties you have the early Ames models purpose built for
>>>> sprinklers readily available, but many units being installed are still
>> not
>>>> listed for fire service as many jurisdictions don't consider the fire
>> line
>>>> a fire line until after the backflow, and a n on-listed device is
>> cheaper
>>>> than a listed one. Plus many go back to the seventies and many used
>> weights
>>>> instead of springs and complicated lever systems for joining the
>> clappers
>>>> and weights. Wish I could post a picture.
>>>> 
>>>> 
>>>> On Tue, Jul 23, 2013 at 7:33 PM, Dwight Havens <[email protected]
>>>>> wrote:
>>>> 
>>>>> Give me a time frame. My best recollection is the mid '90's.
>>>>> 
>>>>> Dwight
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>> ________________________________
>>>>> From: Ron Greenman <[email protected]>
>>>>> To: [email protected]
>>>>> Sent: Tuesday, July 23, 2013 9:12 PM
>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>>>>> 
>>>>> 
>>>>> Were these the plumbing type before fire service listed devices
>> existed.
>>>>> 
>>>>> 
>>>>> On Tue, Jul 23, 2013 at 4:32 PM, Dwight Havens <[email protected]
>>>>>> wrote:
>>>>> 
>>>>>> Yes, yes, and yes.  The original proposal was based on observed
>>>> failures
>>>>>> of BFPAs to operate properly during main drain testing.
>>>>>> 
>>>>>> Glendale, AZ public library specifically comes to mind.
>>>>>> 
>>>>>> Dwight
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> ________________________________
>>>>>> From: Todd Williams <[email protected]>
>>>>>> To: "[email protected]" <
>>>>>> [email protected]>
>>>>>> Sent: Monday, July 22, 2013 9:32 PM
>>>>>> Subject: Re: SIGN for Backflow Prevention Assembly Forward Flow Test
>>>>>> 
>>>>>> 
>>>>>> Has there ever been an instance of system failure due to the backflow
>>>> not
>>>>>> properly opening? How about detection of a BFP problem during a full
>>>> flow
>>>>>> test. How about something subsequent to the initial acceptance?
>>>>>> 
>>>>>> Todd G Williams, PE
>>>>>> Fire Protection Design/Consulting
>>>>>> Stonington, CT
>>>>>> 860-535-2080
>>>>>> www.fpdc.com
>>>>>> 
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> 
>>>>>> 
>>>>> 
>>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> 
>>>>>> 
>>>>> 
>>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>> --
>>>>> Ron Greenman
>>>>> Instructor
>>>>> Fire Protection Engineering Technology
>>>>> Bates Technical College
>>>>> 1101 So. Yakima Ave.
>>>>> Tacoma, WA 98405
>>>>> 
>>>>> [email protected]
>>>>> 
>>>>> http://www.bates.ctc.edu/fireprotection/
>>>>> 
>>>>> 253.680.7346
>>>>> 253.576.9700 (cell)
>>>>> 
>>>>> Member:
>>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>>>> 
>>>>> They are happy men whose natures sort with their vocations. -Francis
>>>> Bacon,
>>>>> essayist, philosopher, and statesman (1561-1626)
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> 
>>>>> 
>>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> 
>>>>> 
>>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> 
>>>> 
>>>> 
>>>> 
>>>> --
>>>> Ron Greenman
>>>> Instructor
>>>> Fire Protection Engineering Technology
>>>> Bates Technical College
>>>> 1101 So. Yakima Ave.
>>>> Tacoma, WA 98405
>>>> 
>>>> [email protected]
>>>> 
>>>> http://www.bates.ctc.edu/fireprotection/
>>>> 
>>>> 253.680.7346
>>>> 253.576.9700 (cell)
>>>> 
>>>> Member:
>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>>> 
>>>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon,
>>>> essayist, philosopher, and statesman (1561-1626)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> 
>>> 
>>> 
>>> 
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> [email protected]
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon,
>>> essayist, philosopher, and statesman (1561-1626)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
> 
> 
> 
> -- 
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to