These are two isolated areas at a hospital - one over some outdoor
seating at the dining common and the other a canopy that covers trash
enclosures and a couple of service enclosures.   Both are a couple
hundred feet from the service entry and if we built a dry riser there,
we don't have enough room to slope the long run of main to the protected
spaces.   The AHJ is one of those state agencies that has <ahem>
interpreted the standard liberally, and they don't want any dry system
that may be downstream of the riser room no matter how it's configured,
so I'm thinking that trace may be an alternative to the auxiliary
drainage and maintenance issues associated with dry-pipe in this
particular application.

Steve 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Bobby Gillett
Sent: Thursday, August 01, 2013 12:03 PM
To: [email protected]
Subject: Re: Heat trace question

Steve,

 I had priced a system about two years ago and learned a lot. I found
the Tyco Raychem system was the best for my scenario; a lot of factors
go in to it - depends on size of piping and length, how much (if any)
insulation will be used, temperatures, and don't forget it has to be
listed for FP and supervised per NFPA 13. We had a local Tyco
distributor work up the pricing
- we gave him our plans and he took it off and priced it. I'm glad he
did.
I would have missed a lot - this was a big system in a 100'-0+ tower
w/standpipes etc.. It ended up needing two panels for supervisory due to
the length of the cables, etc.

Bobby


On Thu, Aug 1, 2013 at 1:53 PM, Steve Leyton
<[email protected]>wrote:

> Help a warm weather brother out please, with recommendations for heat
> trace systems.   Price, reliability, branch line listings?
>
>
>
> Steve Leyton
>
> PROTECTION DESIGN & CONSULTING
>
> 2851 Camino del Rio South, Suite 400
>
> San Diego, CA 92108
>
> -------------------------------------------------------------
>
> Ph:      858.751.2930 - ext. 102
>
> Fax:    858.751.2933
>
> Cell:  619.972.5696
>
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Bobby Gillett
*Living Water Fire Protection, LLC*
1160 McKenzie Rd.
Cantonment, FL 32533
(850) 937-1850
livingwaterfp.com  <http://livingwaterfp.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to