Steve,

Can you split the difference and put a drum drip at the other end? 1/4" per 10' 
of main = 2 1/2" in 100'


 
Thanks,
J. Lewis




>________________________________
> From: Steve Leyton <[email protected]>
>To: [email protected] 
>Sent: Thursday, August 1, 2013 12:15 PM
>Subject: RE: Heat trace question
> 
>
>These are two isolated areas at a hospital - one over some outdoor
>seating at the dining common and the other a canopy that covers trash
>enclosures and a couple of service enclosures.   Both are a couple
>hundred feet from the service entry and if we built a dry riser there,
>we don't have enough room to slope the long run of main to the protected
>spaces.   The AHJ is one of those state agencies that has <ahem>
>interpreted the standard liberally, and they don't want any dry system
>that may be downstream of the riser room no matter how it's configured,
>so I'm thinking that trace may be an alternative to the auxiliary
>drainage and maintenance issues associated with dry-pipe in this
>particular application.
>
>Steve 
>
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>Bobby Gillett
>Sent: Thursday, August 01, 2013 12:03 PM
>To: [email protected]
>Subject: Re: Heat trace question
>
>Steve,
>
>I had priced a system about two years ago and learned a lot. I found
>the Tyco Raychem system was the best for my scenario; a lot of factors
>go in to it - depends on size of piping and length, how much (if any)
>insulation will be used, temperatures, and don't forget it has to be
>listed for FP and supervised per NFPA 13. We had a local Tyco
>distributor work up the pricing
>- we gave him our plans and he took it off and priced it. I'm glad he
>did.
>I would have missed a lot - this was a big system in a 100'-0+ tower
>w/standpipes etc.. It ended up needing two panels for supervisory due to
>the length of the cables, etc.
>
>Bobby
>
>
>On Thu, Aug 1, 2013 at 1:53 PM, Steve Leyton
><[email protected]>wrote:
>
>> Help a warm weather brother out please, with recommendations for heat
>> trace systems.   Price, reliability, branch line listings?
>>
>>
>>
>> Steve Leyton
>>
>> PROTECTION DESIGN & CONSULTING
>>
>> 2851 Camino del Rio South, Suite 400
>>
>> San Diego, CA 92108
>>
>> -------------------------------------------------------------
>>
>> Ph:      858.751.2930 - ext. 102
>>
>> Fax:    858.751.2933
>>
>> Cell:  619.972.5696
>>
>>
>>
>>
>>
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>>
>
>
>
>--
>Bobby Gillett
>*Living Water Fire Protection, LLC*
>1160 McKenzie Rd.
>Cantonment, FL 32533
>(850) 937-1850
>livingwaterfp.com  <http://livingwaterfp.com/>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
>.org
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to