If you call tyco they can probably answer that for you. I was under the 
impression that the given k factor applied to the entire device - so that the 
dry head ended up discharging as if a regular head of the same k factor was 
installed directly.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Spencer 
Allen
Sent: Thursday, August 15, 2013 8:25 AM
To: [email protected]
Subject: Equivalent Length of Dry Sprinkler for Hyd Calcs

Hi Forum,

 

I was wondering if anyone was aware of a manufacturer which published
equivalent lengths of dry sprinklers for use in hydraulic calculations?

 

Best Regards,

 

Spencer Allen

Fire Engineering Solutions | Sprinkler Design & Consultancy

 

 

 

 