I would check with the manufacturer of the specific sprinkler you are proposing 
to install.  Dry sprinklers have internal moving parts and the designs aren't 
necessarily the same between different ones; if there's a measurable added 
friction loss in the barrel from flow over and through the various tube and 
spring assemblies, I'd wager they've got the net K or pressure loss available.  

Steve Leyton


-----Original Message-----
From: [email protected] on behalf of Matt Grise
Sent: Thu 8/15/2013 6:40 AM
To: [email protected]
Subject: RE: Equivalent Length of Dry Sprinkler for Hyd Calcs
 
If you call tyco they can probably answer that for you. I was under the 
impression that the given k factor applied to the entire device - so that the 
dry head ended up discharging as if a regular head of the same k factor was 
installed directly.

Matt Grisé PE*, LEED AP, NICET II  
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Spencer 
Allen
Sent: Thursday, August 15, 2013 8:25 AM
To: [email protected]
Subject: Equivalent Length of Dry Sprinkler for Hyd Calcs

Hi Forum,

 

I was wondering if anyone was aware of a manufacturer which published
equivalent lengths of dry sprinklers for use in hydraulic calculations?

 

Best Regards,

 

Spencer Allen

Fire Engineering Solutions | Sprinkler Design & Consultancy

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to