> Subject: Change Order Form
> 
> Does anyone have a Change Order form in Word they can email to me?
> 
> Thanks
> 
> Forest Wilson
> 
> Sent from my iPhone
> 
> On Aug 15, 2013, at 9:47 AM, "Steve Leyton" <[email protected]> 
> wrote:
> 
>> I would check with the manufacturer of the specific sprinkler you are 
>> proposing to install.  Dry sprinklers have internal moving parts and the 
>> designs aren't necessarily the same between different ones; if there's a 
>> measurable added friction loss in the barrel from flow over and through the 
>> various tube and spring assemblies, I'd wager they've got the net K or 
>> pressure loss available.  
>> 
>> Steve Leyton
>> 
>> 
>> -----Original Message-----
>> From: [email protected] on behalf of Matt Grise
>> Sent: Thu 8/15/2013 6:40 AM
>> To: [email protected]
>> Subject: RE: Equivalent Length of Dry Sprinkler for Hyd Calcs
>> 
>> If you call tyco they can probably answer that for you. I was under the 
>> impression that the given k factor applied to the entire device - so that 
>> the dry head ended up discharging as if a regular head of the same k factor 
>> was installed directly.
>> 
>> Matt Grisé PE*, LEED AP, NICET II  
>> Sales Engineer 
>> Alliance Fire Protection 
>> 130 w 9th Ave.
>> North Kansas City, MO 64116
>> 
>> *Licensed in KS & MO 
>> 
>> 913.888.0647 ph 
>> 913.888.0618 f 
>> 913.927.0222 cell 
>> www. AFPsprink.com 
>> 
>> 
>> -----Original Message-----
>> From: [email protected] 
>> [mailto:[email protected]] On Behalf Of Spencer 
>> Allen
>> Sent: Thursday, August 15, 2013 8:25 AM
>> To: [email protected]
>> Subject: Equivalent Length of Dry Sprinkler for Hyd Calcs
>> 
>> Hi Forum,
>> 
>> 
>> 
>> I was wondering if anyone was aware of a manufacturer which published
>> equivalent lengths of dry sprinklers for use in hydraulic calculations?
>> 
>> 
>> 
>> Best Regards,
>> 
>> 
>> 
>> Spencer Allen
>> 
>> Fire Engineering Solutions | Sprinkler Design & Consultancy
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to