Ahh but we are intermixing reality and assigned methodology.  With all the 
averaging to define the K-factor, applying rectangles to circular discharge 
patterns, differences in losses in fittings, etc etc etc despite using a very 
precise calculation equation, we still are making a rough estimate that works 
very well at ensuring fire control.

Just like the cut-sheet shows, the nominal K-factor is used.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Aug 15, 2013, at 6:47 AM, Steve Leyton <[email protected]> wrote:

> I would check with the manufacturer of the specific sprinkler you are 
> proposing to install.  Dry sprinklers have internal moving parts and the 
> designs aren't necessarily the same between different ones; if there's a 
> measurable added friction loss in the barrel from flow over and through the 
> various tube and spring assemblies, I'd wager they've got the net K or 
> pressure loss available.  
> 
> Steve Leyton