But Tim's 8" minimum lintel creates separate compartments that comprise a
bathroom of the shower only, and a bathroom that does not include the
shower. If both are under 55 sqft separately heads are not required in
either.


On Wed, Oct 2, 2013 at 6:56 AM, Travis Mack <[email protected]> wrote:

> You count the shower space. Been that way for a fee editions now. Maybe
> changed in 99 or 02 edition.
>
> Travis Mack, SET
> MFP Design, LLC
>
> Sent from my iPhone
>
> > On Oct 2, 2013, at 6:47 AM, Todd - Work <[email protected]> wrote:
> >
> > When the square footage is calculated for a bathroom under 13R, does it
> include the square footage of the shower? I say yes, but my client says no.
> It makes the difference of 48 heads on a particular job.
> >
> > Todd G Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > www.fpdc.com
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to