13 (2013) 8.7.3.1.4 seems to support the lintel as a beam.

8.7.3.1.4    Sidewall spray sprinklers shall not be installed back-to-back 
without being separated by a continuous lintel or soffit.

Ron F


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
rongreenman .
Sent: Wednesday, October 02, 2013 5:09 PM
To: [email protected]
Subject: Re: showers included in bathroom area

Yes, I'm wrestling with that beam in, say, a living room. It's an obstruction, 
it's kind of a compartment, it kind of compartmentalizes the room, but...? So 
if it's a lintel, defined as a "beam" over a door it doesn't compartmentalize 
one section from another if there's no wall to either side, but it does if 
there is wall, no matter how short? If there's a shower door does that count? 
What about that living room beam with two feet of wall on either end of a 
sixteen foot free span, with the architect calling one side living and the 
other dining? I think tis can be pretty shaky stuff for literalists.


On Wed, Oct 2, 2013 at 12:33 PM, Roland Huggins
<[email protected]>wrote:

> the same logic would say a beam in the middle of a room make it two 
> compartments.  If you have a 8" obstruction on two sides of the shower 
> but no portion of either span is a wall, then it isn't a lintel.
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Oct 2, 2013, at 11:32 AM, "rongreenman ." <[email protected]>
> wrote:
>
> > If there is at least eight inches on both sides I'd argue that it
> separates
> > compartments. If not it's something else. Since it defines an 
> > overhead separation between compartments it is a portal from one to 
> > the other and therefore a doorway. If someone wants to argue 
> > otherwise I'm open to persuasion.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to