NFPA 14, 2010/2013, ยง5.6.1 - Waterflow alarm is required for every standpipe 
system except for manual dry systems.

Steve L




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Friday, October 11, 2013 9:51 AM
To: [email protected]
Subject: Standpipe Flow Switch

NFPA 14 has diagrams (A.7.1(a) '10 ed) of SP systems with pumps that have a 
flow switch shown in the supply pipe from the pump to the SP distribution main. 
I can't find anything in the body that requires a "master flow switch". Is the 
flow switch only required when there is a pump?

Ron F