Steve,

Would the intent of 5.6.1 be met if there were flow switches on floor
control valves  with the required inspector's test for them?

It also says Standpipe System - not standpipe, so is the intent as it
sounds that one flow switch would satisfy the requirement for more that one
individual standpipe that are interconnected?


Thanks,
Greg


On Fri, Oct 11, 2013 at 11:58 AM, <[email protected]> wrote:

> Thanks Steve. Guess I was doing some Friday speed reading. Going back to
> sleep now.
>
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Steve Leyton
> Sent: Friday, October 11, 2013 9:56 AM
> To: [email protected]
> Subject: RE: Standpipe Flow Switch
>
> NFPA 14, 2010/2013, ยง5.6.1 - Waterflow alarm is required for every
> standpipe system except for manual dry systems.
>
> Steve L
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of
> [email protected]
> Sent: Friday, October 11, 2013 9:51 AM
> To: [email protected]
> Subject: Standpipe Flow Switch
>
> NFPA 14 has diagrams (A.7.1(a) '10 ed) of SP systems with pumps that have
> a flow switch shown in the supply pipe from the pump to the SP distribution
> main. I can't find anything in the body that requires a "master flow
> switch". Is the flow switch only required when there is a pump?
>
> Ron F
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Greg McGahan
Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to