Thanks Steve. Guess I was doing some Friday speed reading. Going back to sleep now.
Ron F -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Friday, October 11, 2013 9:56 AM To: [email protected] Subject: RE: Standpipe Flow Switch NFPA 14, 2010/2013, ยง5.6.1 - Waterflow alarm is required for every standpipe system except for manual dry systems. Steve L -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, October 11, 2013 9:51 AM To: [email protected] Subject: Standpipe Flow Switch NFPA 14 has diagrams (A.7.1(a) '10 ed) of SP systems with pumps that have a flow switch shown in the supply pipe from the pump to the SP distribution main. I can't find anything in the body that requires a "master flow switch". Is the flow switch only required when there is a pump? Ron F _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org