That is indeed what it means.  We submitted the proposal on this issue a couple 
of cycles ago and the justification states it in just that fashion.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Oct 14, 2013, at 8:12 AM, <[email protected]> wrote:

> 8.3.2.1*   Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or 8.3.2.5 
> are met, ordinary- and intermediate-temperature sprinklers shall be used 
> throughout buildings.
> 
> Does this mean that we can use intermediate temp QR's throughout a LH 
> occupancy? This would eliminate the need to figure out where intermediates 
> are needed because of heat sources.
> 
> Ron F
> 