Check with the manufacturer first.  We've found that some don't stock
nearly as many 175s as they do 155s and 200s.  So if you need the heads
right away, you might be out of luck.


Benjamin Young


On Mon, Oct 14, 2013 at 11:48 AM, <[email protected]> wrote:

> Thanks for the reply. There were some doubters here that wanted to see
> confirmation from another source.
>
> Ron F
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Roland
> Huggins
> Sent: Monday, October 14, 2013 8:31 AM
> To: [email protected]
> Subject: Re: Ordinary vs intermediate temperature heads
>
> That is indeed what it means.  We submitted the proposal on this issue a
> couple of cycles ago and the justification states it in just that fashion.
>
>
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org
>
>
>
>
>
> On Oct 14, 2013, at 8:12 AM, <[email protected]> wrote:
>
> > 8.3.2.1*   Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or
> 8.3.2.5 are met, ordinary- and intermediate-temperature sprinklers shall be
> used throughout buildings.
> >
> > Does this mean that we can use intermediate temp QR's throughout a LH
> occupancy? This would eliminate the need to figure out where intermediates
> are needed because of heat sources.
> >
> > Ron F
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to