Still, having been born and raised in The Show Me State, I had to see for
myself. I now think the activation time difference between a 155F QR and a
200F QR is about 6 seconds per foot of ceiling height. This is based on what
I believe is the low end of NFPA 13, 5.1 through 5.3 (any modern edition)
for quantity, combustibility, and heat release rate. Also based on heads at
20x20 (~14' radial distance from center of plume) using 10' through 20'
ceiling height. So a max of one minute longer, in the big scheme of things
DOES seem insignificant to me... too.

Brad Casterline, S.E.T. 

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Monday, October 14, 2013 2:25 PM
To: '[email protected]'
Subject: RE: Ordinary vs intermediate temperature heads

Even I can understand that Roland, thanks, I got my mind right now ;)

-----Original Message-----
From: Roland Huggins [mailto:[email protected]] 
Sent: Monday, October 14, 2013 1:49 PM
To: [email protected]
Subject: Re: Ordinary vs intermediate temperature heads

When the technical committee says so or the AHJ agrees with your variance.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Oct 14, 2013, at 10:37 AM, Brad Casterline <[email protected]>
wrote:

> What I find mind-boggling is "at what point does the time difference
become
> insignificant"?  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to