Still, having been born and raised in The Show Me State, I had to see for myself. I now think the activation time difference between a 155F QR and a 200F QR is about 6 seconds per foot of ceiling height. This is based on what I believe is the low end of NFPA 13, 5.1 through 5.3 (any modern edition) for quantity, combustibility, and heat release rate. Also based on heads at 20x20 (~14' radial distance from center of plume) using 10' through 20' ceiling height. So a max of one minute longer, in the big scheme of things DOES seem insignificant to me... too.
Brad Casterline, S.E.T. -----Original Message----- From: Brad Casterline [mailto:[email protected]] Sent: Monday, October 14, 2013 2:25 PM To: '[email protected]' Subject: RE: Ordinary vs intermediate temperature heads Even I can understand that Roland, thanks, I got my mind right now ;) -----Original Message----- From: Roland Huggins [mailto:[email protected]] Sent: Monday, October 14, 2013 1:49 PM To: [email protected] Subject: Re: Ordinary vs intermediate temperature heads When the technical committee says so or the AHJ agrees with your variance. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Oct 14, 2013, at 10:37 AM, Brad Casterline <[email protected]> wrote: > What I find mind-boggling is "at what point does the time difference become > insignificant"? _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org