A couple of finer points of my questioning is: 1) Ron asked "...throughout a LH occupancy"?, and L.H. and Residential are two separate classifications. 2) The reasoning in the commentary is that Int. Temp. Q.R. is similar to Ord. Temp. S.R. for activation time, but Residential heads were "born Q.R." and survival in the room of origin was the goal, unlike L.H. occupancies, which would tolerate activation times better that Res. heads could.
I'll be out of the office all day, so thanks in advance for feedback! Brad C -----Original Message----- From: Brad Casterline [mailto:[email protected]] Sent: Wednesday, December 11, 2013 3:21 PM To: [email protected] Subject: RE: Ordinary vs intermediate temperature heads The original reference by Ron F. below is from NFPA 13-2010. I am now wondering if the response by Roland would indeed apply "...throughout buildings". Specifically, can we use intermediate temp residential heads in a dorm room even if far enough away from a heat source to use ordinary temp? 8.3.2.5* (8) makes me wonder, even though it is lumped with other than residential areas (or maybe because it is!). thanks, Brad -----Original Message----- From: [email protected] [mailto:[email protected]] Sent: Monday, October 14, 2013 10:48 AM To: [email protected] Subject: RE: Ordinary vs intermediate temperature heads Thanks for the reply. There were some doubters here that wanted to see confirmation from another source. Ron F -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Monday, October 14, 2013 8:31 AM To: [email protected] Subject: Re: Ordinary vs intermediate temperature heads That is indeed what it means. We submitted the proposal on this issue a couple of cycles ago and the justification states it in just that fashion. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Oct 14, 2013, at 8:12 AM, <[email protected]> wrote: > 8.3.2.1* Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or 8.3.2.5 are met, ordinary- and intermediate-temperature sprinklers shall be used throughout buildings. > > Does this mean that we can use intermediate temp QR's throughout a LH occupancy? This would eliminate the need to figure out where intermediates are needed because of heat sources. > > Ron F > _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org