A couple of finer points of my questioning is:

1) Ron asked "...throughout a LH occupancy"?, and L.H. and Residential are
two separate classifications.
2) The reasoning in the commentary is that Int. Temp. Q.R. is similar to
Ord. Temp. S.R. for activation time, but Residential heads were "born Q.R."
and survival in the room of origin was the goal, unlike L.H. occupancies,
which would tolerate activation times better that Res. heads could.

I'll be out of the office all day, so thanks in advance for feedback!

Brad C 

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Wednesday, December 11, 2013 3:21 PM
To: [email protected]
Subject: RE: Ordinary vs intermediate temperature heads

The original reference by Ron F. below is from NFPA 13-2010.

I am now wondering if the response by Roland would indeed apply
"...throughout buildings". Specifically, can we use intermediate temp
residential heads in a dorm room even if far enough away from a heat source
to use ordinary temp? 8.3.2.5* (8) makes me wonder, even though it is lumped
with other than residential areas (or maybe because it is!).

thanks,
Brad

-----Original Message-----
From: [email protected] [mailto:[email protected]] 
Sent: Monday, October 14, 2013 10:48 AM
To: [email protected]
Subject: RE: Ordinary vs intermediate temperature heads

Thanks for the reply. There were some doubters here that wanted to see
confirmation from another source.

Ron F

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Monday, October 14, 2013 8:31 AM
To: [email protected]
Subject: Re: Ordinary vs intermediate temperature heads

That is indeed what it means.  We submitted the proposal on this issue a
couple of cycles ago and the justification states it in just that fashion.


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org

On Oct 14, 2013, at 8:12 AM, <[email protected]> wrote:

> 8.3.2.1*   Unless the requirements of 8.3.2.2, 8.3.2.3, 8.3.2.4, or
8.3.2.5 are met, ordinary- and intermediate-temperature sprinklers shall be
used throughout buildings.
> 
> Does this mean that we can use intermediate temp QR's throughout a LH
occupancy? This would eliminate the need to figure out where intermediates
are needed because of heat sources.
> 
> Ron F
> 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to