WoW! If they are fixed in place and you have to sprinkler under you will
need about what, (12) heads/table, and baffles; with 6 or 8 inches from
bottom of framing to floor the floor is an obstruction to the pattern
developing for uniform density, unless the spacing is very close ;) .
Maybe some day the book will say unless the depth of the space exceeds max
deflector distance, heads are not required. You cold def use QR Reduction
though (if you use QR heads and wet pipe, but the fuel load itself will also
be an obstruction!

never mind me though as usual-- i'm just geeking here

-----Original Message-----
From: Johnson, Duane (NIH/OD/ORS) [C] [mailto:[email protected]] 
Sent: Thursday, December 12, 2013 3:04 PM
To: [email protected]
Subject: RE: obstruction vs concealed space.

8.5.5.3.2 Sprinklers shall not be required under obstructions that are not
fixed in place, such as conference tables.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Todd - Work [mailto:[email protected]] 
Sent: Thursday, December 12, 2013 4:02 PM
To: [email protected]
Subject: Re: obstruction vs concealed space.

NFPA 13 (2002) section 8.5.5.3.1 and equivalent sections of subsequent
editions.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Dec 12, 2013, at 3:47 PM, Steven Scandaliato <[email protected]>
wrote:
> 
> What is making you feel you need to put sprinklers under tables that are
16"
> off the floor? Or under "normal" circumstances? 
> 
> Steven Scandaliato, SET CFPS
> 520.971.2322 Cell
> Skype: steven.scandaliato
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of 
> Todd - Work
> Sent: Thursday, December 12, 2013 2:19 PM
> To: [email protected]
> Subject: Re: obstruction vs concealed space.
> 
> Growing tables in an agricultural facility
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
> 
>> On Dec 12, 2013, at 2:57 PM, <[email protected]> wrote:
>> 
>> What kind of "tables", what kind of environment?
>> 
>> Craig L. Prahl, CET   
>> Fire Protection Group Lead
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>> 
>> 
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of 
>> Todd - Work
>> Sent: Thursday, December 12, 2013 2:34 PM
>> To: [email protected]
>> Subject: obstruction vs concealed space.
>> 
>> I am working on a project where they are going to have 9 ft x 20 ft 
>> tables
> located 16" off the floor. Not sure if the tables will be built with 
> 2x8 or
> 2x10 framing. Under normal circumstances, we would need to have 
> sprinklers installed under the tables. However, if the distance from 
> the bottom of the joist to the floor is 6" or less, could it be considered
a "concealed space"
> and sprinkler be eliminated? I would assume if those sprinklers were 
> eliminated, the design area for the ceiling would increase to 3000 sqft.
>> 
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> www.fpdc.com
>> 860-535-2080 (ofc)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>> l
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to