Todd,

In thinking more about this, just a couple thoughts to throw out--

1)The combustible concealed spaces that pose a challenge are usually 'finish
work' for architectural reasons up off the floor and hiding the structure.
If a fire gets inside it can grow unnoticed and cause structural damage and
pose a huge threat. A Table is not like that.
2) Imagine a stack of idle pallets as the fuel load, and the 1st one starts
16" off the floor somehow; we would not sprinkler under the 1st pallet- we
would plan a water flow rate to control the fuel load. In the same way I see
the combustible table itself as the fuel load, and not what very small
ignition source might be under it.

Of course, I cannot not cite any code sections other that the one that says
something about providing "...a reasonable degree of protection...".

Brad


-----Original Message-----
From: Todd - Work [mailto:[email protected]] 
Sent: Thursday, December 12, 2013 4:29 PM
To: [email protected]
Subject: Re: obstruction vs concealed space.

Probably require concealed space sprinklers

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Dec 12, 2013, at 4:27 PM, "Brad Casterline" <[email protected]>
wrote:
> 
> WoW! If they are fixed in place and you have to sprinkler under you will
> need about what, (12) heads/table, and baffles; with 6 or 8 inches from
> bottom of framing to floor the floor is an obstruction to the pattern
> developing for uniform density, unless the spacing is very close ;) .
> Maybe some day the book will say unless the depth of the space exceeds max
> deflector distance, heads are not required. You cold def use QR Reduction
> though (if you use QR heads and wet pipe, but the fuel load itself will
also
> be an obstruction!
> 
> never mind me though as usual-- i'm just geeking here
> 
> -----Original Message-----
> From: Johnson, Duane (NIH/OD/ORS) [C] [mailto:[email protected]] 
> Sent: Thursday, December 12, 2013 3:04 PM
> To: [email protected]
> Subject: RE: obstruction vs concealed space.
> 
> 8.5.5.3.2 Sprinklers shall not be required under obstructions that are not
> fixed in place, such as conference tables.
> 
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor)
> Office of Research Services 
> National Institutes of Health 
> 301-496-0487
> 
> "Protecting Science - One Sprinkler at a Time"
> 
> 
> -----Original Message-----
> From: Todd - Work [mailto:[email protected]] 
> Sent: Thursday, December 12, 2013 4:02 PM
> To: [email protected]
> Subject: Re: obstruction vs concealed space.
> 
> NFPA 13 (2002) section 8.5.5.3.1 and equivalent sections of subsequent
> editions.
> 
> Todd G Williams, PE
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to