Go back to those old examples of fixed cutting tables that accompany that
rule. Meat--It's the fat that accumulates under the table to be swept up
and rendered later. Textiles--lots of cloth kindling. Etcetera. Then we're
typically talking about industrial production level stuff, not conference
tables. Go back to Mark Sornsin's comments. We need to get this image of a
floor gridded off in one foot sections getting an exact and even
distribution of 0.15 gallons per minute out of our heads. If I can keep the
conference table on fire confined to 1500 sqft (that's a big table) until
the FD arrives then I suspect whatever stray scrap paper may have fallen
under it won't be a big contributor to extended growth. Now a day's
accumulation of cotton scraps and thread fibers.... That's  adifferent
story altogether.


On Fri, Dec 13, 2013 at 7:08 AM, Todd Williams <[email protected]> wrote:

> Good thought, but you could end up with a shielded fire which the
> sprinklers at the ceiling may not be able to contain. EH2 addresses this
> type of fire to certain degree as does the 3000 sqft remote area
> requirement for adjacent areas
>
> I don't think the idle pallet comparison is viable because you don't have
> a solid top.
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080
> www.fpdc.com
>
>
> > On Dec 13, 2013, at 8:54 AM, "Brad Casterline" <[email protected]>
> wrote:
> >
> > Todd,
> >
> > In thinking more about this, just a couple thoughts to throw out--
> >
> > 1)The combustible concealed spaces that pose a challenge are usually
> 'finish
> > work' for architectural reasons up off the floor and hiding the
> structure.
> > If a fire gets inside it can grow unnoticed and cause structural damage
> and
> > pose a huge threat. A Table is not like that.
> > 2) Imagine a stack of idle pallets as the fuel load, and the 1st one
> starts
> > 16" off the floor somehow; we would not sprinkler under the 1st pallet-
> we
> > would plan a water flow rate to control the fuel load. In the same way I
> see
> > the combustible table itself as the fuel load, and not what very small
> > ignition source might be under it.
> >
> > Of course, I cannot not cite any code sections other that the one that
> says
> > something about providing "...a reasonable degree of protection...".
> >
> > Brad
> >
> >
> > -----Original Message-----
> > From: Todd - Work [mailto:[email protected]]
> > Sent: Thursday, December 12, 2013 4:29 PM
> > To: [email protected]
> > Subject: Re: obstruction vs concealed space.
> >
> > Probably require concealed space sprinklers
> >
> > Todd G Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > www.fpdc.com
> > 860-535-2080 (ofc)
> >
> >>> On Dec 12, 2013, at 4:27 PM, "Brad Casterline" <
> [email protected]>
> >> wrote:
> >>
> >> WoW! If they are fixed in place and you have to sprinkler under you will
> >> need about what, (12) heads/table, and baffles; with 6 or 8 inches from
> >> bottom of framing to floor the floor is an obstruction to the pattern
> >> developing for uniform density, unless the spacing is very close ;) .
> >> Maybe some day the book will say unless the depth of the space exceeds
> max
> >> deflector distance, heads are not required. You cold def use QR
> Reduction
> >> though (if you use QR heads and wet pipe, but the fuel load itself will
> > also
> >> be an obstruction!
> >>
> >> never mind me though as usual-- i'm just geeking here
> >>
> >> -----Original Message-----
> >> From: Johnson, Duane (NIH/OD/ORS) [C] [mailto:[email protected]]
> >> Sent: Thursday, December 12, 2013 3:04 PM
> >> To: [email protected]
> >> Subject: RE: obstruction vs concealed space.
> >>
> >> 8.5.5.3.2 Sprinklers shall not be required under obstructions that are
> not
> >> fixed in place, such as conference tables.
> >>
> >> Duane Johnson, PE
> >> Program Manager
> >> Division of the Fire Marshal (Contractor)
> >> Office of Research Services
> >> National Institutes of Health
> >> 301-496-0487
> >>
> >> "Protecting Science - One Sprinkler at a Time"
> >>
> >>
> >> -----Original Message-----
> >> From: Todd - Work [mailto:[email protected]]
> >> Sent: Thursday, December 12, 2013 4:02 PM
> >> To: [email protected]
> >> Subject: Re: obstruction vs concealed space.
> >>
> >> NFPA 13 (2002) section 8.5.5.3.1 and equivalent sections of subsequent
> >> editions.
> >>
> >> Todd G Williams, PE
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to