Probably require concealed space sprinklers

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Dec 12, 2013, at 4:27 PM, "Brad Casterline" <[email protected]> 
> wrote:
> 
> WoW! If they are fixed in place and you have to sprinkler under you will
> need about what, (12) heads/table, and baffles; with 6 or 8 inches from
> bottom of framing to floor the floor is an obstruction to the pattern
> developing for uniform density, unless the spacing is very close ;) .
> Maybe some day the book will say unless the depth of the space exceeds max
> deflector distance, heads are not required. You cold def use QR Reduction
> though (if you use QR heads and wet pipe, but the fuel load itself will also
> be an obstruction!
> 
> never mind me though as usual-- i'm just geeking here
> 
> -----Original Message-----
> From: Johnson, Duane (NIH/OD/ORS) [C] [mailto:[email protected]] 
> Sent: Thursday, December 12, 2013 3:04 PM
> To: [email protected]
> Subject: RE: obstruction vs concealed space.
> 
> 8.5.5.3.2 Sprinklers shall not be required under obstructions that are not
> fixed in place, such as conference tables.
> 
> Duane Johnson, PE
> Program Manager
> Division of the Fire Marshal (Contractor)
> Office of Research Services 
> National Institutes of Health 
> 301-496-0487
> 
> "Protecting Science - One Sprinkler at a Time"
> 
> 
> -----Original Message-----
> From: Todd - Work [mailto:[email protected]] 
> Sent: Thursday, December 12, 2013 4:02 PM
> To: [email protected]
> Subject: Re: obstruction vs concealed space.
> 
> NFPA 13 (2002) section 8.5.5.3.1 and equivalent sections of subsequent
> editions.
> 
> Todd G Williams, PE