"Hello All,

Would not the test point to test the forward flow of the backflow preventer at 
system demand do the same thing as the main drain before the pump?

Thursday, December 12, 2013, 4:07:24 PM, you wrote:

> You would want a main drain where it is installed so the system can
> be drained for maintenance, hence the word drain. Do you need
> another drain on the suction side of a pump for a test to verify
> condition? There is some merit to that idea. 

> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)

>> On Dec 12, 2013, at 3:49 PM, "Tom Duross" <[email protected]> wrote:

>> I'm looking for opinions on this.

>> A new building I just took over ITM on has a fire pump feeding combination
>> standpipes, fully sprinklered high-rise circa 1974.
>> Existing 2" main drain is toast, handle broken, stem all chewed up from
>> wrenching.
>> I proposed we change it, use a 300# ball valve, galvy pipe; do it right.
>> BUT, it's on the system riser off the pump discharge and I say wrong
>> location.
>> Even the standard still says do a main drain test when you have a fire pump
>> (imho silly), so I do.
>> A main drain test is to verify supply condition.  I say with it where it is,
>> we either have to drop the building to street pressure OR do a main drain
>> with the pump running.  In a case like this I always do the latter but I see
>> others dropping the building and I think it's unnecessary and an impairment.
>> The problem I have with doing 150-200# main drain tests is they do dump a
>> ton of water, even with a fire hose off the 2" el and a hose monster.
>> I feel it's overkill and unnecessary on top of a waste of time but whatever.
>> My issue (finally) is where to properly place a main drain when you have a
>> pump.  I say on the street side bypass supply, just flow supply pressure and
>> be done with it.  Facilities guy says others dumped building and just do
>> that.
>> Sprinklers are tested with the pump running, last few companies shut it off
>> and went on jockey, that's why they're gone.
>> Looking for opinions and even second opinions (ok you're ugly too).
>> What's the proper location?

>> TD

>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


-- 
Best regards,
 Charles                            mailto:[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to