I think we need to go back to the whys. As Duane found the main drain's
purpose is for draining the system, with any necessary auxiliary drain
plugs or valves for draining trapped portions. The "Main Drain Test" has
nothing to do with this but is for establishing a baseline of conditions
(static pressure when closed and residual pressure when open) pertinent to
the water supply at the time of installation. The subsequent tests are to
compare the data now to the original data (baseline). I think earlier in
this discussion, or in that other recent main drain thread, we established
that the main drain needs to be somewhere on the vertical or horizontal
portion of the supply riser before the first split. I think we also agree
that for the "main drain test" we need to use the main drain. I'd suggest
then that for the test it is irrelevant whether the test point (main drain)
is before or after the pump, or whether the pump is running or not, as long
as the conditions of the test (point of test, pump on or off, and I'd add
time of day and whether weekend or weekday depending on the normal demands
on the city loop relative to the original test day and time) for today's
test duplicate the conditions for the baseline test.

Think of tire pressure as an analogy. The recommended (baseline) pressure
is always under a certain load and with hot (in use) tires. Checking
pressure early in the morning after a snow night, before you even start the
car up will give you a low pressure reading if on the way home yesterday
you checked at the gas station close to your home after a twenty minute
drive and made them perfect.


On Fri, Dec 13, 2013 at 7:31 AM, Smith, Steven D. (CSFD) <
[email protected]> wrote:

> I can vouch for this as I had the honor and privilege to work for him a
> while back!
>
> Steve
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Matsuda,
> Richard
> Sent: Friday, December 13, 2013 8:26 AM
> To: [email protected]
> Subject: RE: Fire Pump Room Main Drain
>
> This subject has been a pet-peeve of mine for the past 35 years.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)