What drain? I come out of a jockey with a relief, check, gate and tie to high side of the pump bypass.
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Thursday, December 12, 2013 6:21 PM To: [email protected] Subject: RE: Fire Pump Room Main Drain Why not just use the drain on the JP discharge line. That would verify the supply side connection and give a relative performance over time, without wasting a ton of water. Mark at Aero -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matsuda, Richard Sent: Thursday, December 12, 2013 2:40 PM To: [email protected] Subject: RE: Fire Pump Room Main Drain Tom, Here is a comment that we include on our plan review for all systems that have a fire pump. We require this drain on the suction side of the pump to test/verify in integrity of the incoming water supply. "A main drain test connection must be installed on the suction side of the pump per NFPA-13 (2002 edition), paragraph 8.16. 4.1." rick matsuda city of dallas _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org