You're good at 108 sq. ft.

Jimmy Waite, CET - Design Manager
Fire & Life Safety America- Raleigh District
7711 Welborn Street, Suite 103
Raleigh, NC  27615
Office: 919-872-3250
Cell: 919-868-3546
Fax: 919-877-5775
www.flsamerica.com




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Gregory 
Lindholm
Sent: Friday, February 14, 2014 9:40 AM
To: SprinklerFORUM
Subject: Spacing with sloped piping

We are having a discussion in our office about sprinkler head coverage with 
sloped piping. If we have an area where the branch lines are spaced 13'-7" 
apart, and the heads on the branch lines are 9'-10" apart on the slope (133.39 
sq. ft./ head). The actual floor coverage is 13'-7" x 8'-0" (108.64 sq. ft./ 
head).

We are designing for OH Group II occupancy per NFPA #13 - 2013 (130 sq. ft. / 
head). Section 23.4.4.5.5 says that we design for the projected horizontal 
area, which we assume to mean the actual floor area here. Are we OK with the 
108.64 sq. ft., or does the sloped area of 133.39 cause a problem?

Greg Lindholm
Fire Protection Project Manager
Howe Heating & Plumbing, Inc.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

________________________________

The information contained in this email and any attached documents may contain 
information that is the confidential property of Fire & Life Safety America, 
Inc ("FLSA"). Any documents created on any FLSA computer or by any employee in 
the conduct of FLSA business is work product and owned by FLSA. If the reader 
of this message is not the intended recipient, or the employee or agent 
responsible to deliver it to the intended recipient, you are hereby notified 
that any dissemination, distribution or other use of the contents of this 
communication is strictly prohibited. If you have this communication in error, 
please immediately notify the sender and delete this email.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to