As per NFPA 20-2013:    4.7.7.1   The net pump shutoff (churn) pressure plus 
the maximum static suction pressure, adjusted for elevation, shall not exceed 
the pressure for which the system components are rated.


So yes it is only by 3 psi, but you are crossing that line in the sand.

Since your only components that aren't rated for more than 175 psi are the 
sprinklers, why not use high pressure sprinklers instead. I know that both 
Viking (250 psi) and Reliable (300 psi) have those. Using sprinklers rated for 
250 psi or 300 psi would be a lot more convenient for all parties than using 
pressure reducing valves. 

Larry Keeping, P.Eng.

Professional Loss Control
3413 Wolfedale Road, Suite 6
Mississauga, Ontario
L5C 1V8

Phone:   905-949-2755, ext. 204
Fax:        905-949-1752

E-mail:    [email protected]

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matsuda, 
Richard
Sent: February-18-14 4:22 PM
To: [email protected]
Subject: RE: Static Pressure/Working Pressure


 Ron,

1. The engr firm is correct...anything over 175-psi requires a PRV and the 
maximum expected static pressure (churn pressure) is used to determine where 
the PRV's are required.

2. If you do not put the PRV and something starts to leak and cause water 
damage, then you will assume responsibility.

3. I agree with you 100%...that the churn pressure only exists during the pump 
tests and that a city water supply may vary as much as 10 to 15-psi during the 
day so most of the time it will actually be less than 175-psi. 

4. I also feel that installing a PRV for the "excessive" 3-psi is a waste of 
time and money. The hydrant test was done with a gauge that was bouncing around 
between 4 to 6-psi, and what if it was only 176-psi instead of 178-psi. 
However, I am not the responsible party to address this issue from a liability 
perspective.
rick

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, February 18, 2014 1:50 PM
To: [email protected]
Subject: Static Pressure/Working Pressure

3.8.1.9.2 Static Pressure. The pressure that exists at a given point under 
normal distribution system conditions measured ...
We have a project with an electric pump and when combined with the current 
water supply the churn pressure is 178 psi. A nationally known engineering firm 
wants us to install PRV's on the lowest level of the building because of the 3 
psi. Our position is that the pressure only exists at churn and that is similar 
to an overnight pressure surge in a municipal water system. The over pressure 
will be compensated for by the pressure relief valves once the pump stops. Are 
we being overly loose with our interpretation of "normal" or is the engineering 
firm correct?
Ron F  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to