Sometimes there seems to be more sprinkler scientists than sprinkler engineers.
Ron F

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
rongreenman .
Sent: Tuesday, February 18, 2014 3:58 PM
To: [email protected]
Subject: Re: Static Pressure/Working Pressure

On Tue, Feb 18, 2014 at 2:16 PM, <[email protected]> wrote:



> "after all it's a parking garage"


And there you have it. If you're not concerned about full flowing PRVs who 
cares about an occasional leaking sprinkler because it was 178 psi instead of 
175 psi? I think the owner, the insurer, the engineer, the architect, and the 
AHJ need a "come to Jesus meeting" meeting and look at this rationally. Per 
ABET, "Engineering is the profession in which a knowledge of the mathematical 
and natural sciences gained by study, experience, and practice is applied with 
judgment to develop ways to utilize, economically, the materials and forces of 
nature for the benefit of mankind." I'm missing the "experience and practice 
applied with judgement" to "economically benefit mankind," part here.



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list