Just a few comments.

" Why? Because the thinking was that many fire departments don't have the 
knowledge or expertise to specify engineering criteria and that's likely true." 
I couldn't disagree more with that logic in this regard, they can hand an EOR 
what they use at the least and the EOR can figure out what the pressure needs 
to be (or they shouldn't be an EOR).  All FD's have the key to the fire house 
door, THAT is all that is required. IMHO this is a cover excuse for something 
else.  

The problem with 14 is I never HAVE to talk to the FD.  (I'm out on a limb here 
as I don't have the current edition handy).  It says 100 or 65 per AHJ, right.  
I design 100 and am perfectly in compliance.  Fire chief can jump up and down 
all he/she wants and unless there is an ordinance (which are incredibly rare) 
it is nothing but exercise for them and $ for a justifiable change order to the 
owner if they CHOOSE to comply. That is why the standard is 20 years, 20 YEARS, 
behind in stripping out all pressure and forcing a EOR or designer to talk to 
the FD. 

I respect the FD changing it up in the future but at least at one time it 
worked.  There are, I'd bet, a majority of systems out there that have never 
worked. NFPA 25 should be changed to have a question answered by FD - have the 
attack hoses/nozzles changed since the last inspection?  If no carry on.  If 
yes direct the owner to engage competent EOR or designer to evaluate the  
current standpipe.  Yeah a little unfair to building owners to have to spend 
money every time the FD tinkers around with the attack lines. 

Not ranting at you Steve, I know you are the messenger (and have access to the 
committee the we mere mortals do not).

Chris Cahill, PE*
Associate Fire Protection Engineer 
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Steve 
Leyton
Sent: Wednesday, February 19, 2014 4:44 PM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

I've been out of the office all day, so not able to respond until now.
Have even gotten a couple of emails from peeps wondering why I haven't chimed 
in yet, so I picked Scan's mail as a basis for reply because it most 
efficiently summarizes my own boiled down philosophy, with one
caveat.   I agree with the early posts from this morning's onset of the
thread, and the information presented so far is accurate and consistent
with the committee's intent, methinks.   A few clarifications and
enhancements:

I have rep'd AFSA on the 14 since '99 or 2000, so don't have personal knowledge 
of what happened in the '93 cycle.  However (to drop a few names), I have had 
the chance over the years to talk with some people who were either on the 
committee or have personal knowledge of how it came down, such as former NFPA 
staff liaison David Hague, committee
members Maurice Pilette, Jeffry Shapiro and Chet Schirmer.   As Jim
previously stated, the 65psi rule in earlier editions was based on fixed bore 
nozzles and 65psi was enough to allow friction loss in the hose and still give 
a good pattern and throw distance from a straight stream tip.
But fire departments were seizing on the still-relatively-new Elkhart
Select-A-Flow nozzles and they were rated for 100psi at the tip.   So
the thinking was that if you calculated friction loss at 250gpm through
1-3/4" and 2-1/2" hose, you'd need at least 125psi and perhaps 150.   If
you split the flow, 125gpm through each of 2 1-1/2" attack lines will cause up 
to 50psi of loss as well, so the idea was originally to bump it
to 150.   And there was much rejoicing by the pump people ...   But it
became apparent that such a radical upgrade would get NITMAM'd out of the room 
at the code hearing so the TC arrived at 100psi as a good
compromise.   Not terribly scientific but strategically sound and it
wasn't challenged.  But that pressure may or may not be adequate for all 
tactical op's and as others have already said, you need to correspond with the 
fire department to be sure of what they need or want.

So why didn't we change the standard to mandate that it be purely
performance based?   We fielded two proposals two cycles ago that would
have made higher pressure and/or FD specification of pressure the norm, but 
both were voted down and the annex language added instead.  Why?
Because the thinking was that many fire departments don't have the knowledge or 
expertise to specify engineering criteria and that's likely
true.   Some FPO's don't even know what their trucks are carrying for
equipment.   Elkhart now makes selectable nozzles in 100psi
(Select-A-Flow) and 75psi (Phantom) classes.   They also make the Chief,
which is a 50psi tip.  Task force makes a tip that is selectable flow AND 
pressure in 50-75-100 psi settings, so it's incredibly versatile and will 
function across a wide range of water supply.  But it costs a lot more than 
Brands X, Y and Z.  Akron Brass makes a tip that will handle up to 500psi, 
which feeds into the HP trend we're seeing across the
board (think mist).   Clark County FD in Las Vegas is experimenting with
standpipe working pressures up to 400psi at their training center, if
I'm not mistaken.   It should be performance based yes, but the EOR or
designer of record should be prepared to design per the prescription if
that's the fall back.   Should it be higher?   Yes ... maybe ... <shrug
of shoulders>.   Anyway and bottom line, instead of prescribing higher
pressures or a go-to with the fire department, we added A7.8 and I will take 
credit for writing at least half of it myself.  I'm not happy with the table as 
it's confusing and poorly worded; the most common high-rise tactic as best as I 
can tell is to drop a 6-8' section of 2-1/2" rubber hose on the deck and 
connect a 2-1/2" x 1-1/2" x 1-1/2" gated wye, and
then run one or two 1-1/2" attack lines flowing 125-175gpm.   This
configuration will likely impart at least 40psi of friction loss up to 55psi, 
depending on variables.  So for a 75psi tip you'd want at least 115-120psi at 
the valve, or more.  For a 100psi tip it could easily be
higher.      

Another thing to consider in high-rise buildings (that was mentioned on this 
thread) is pressure reducing valves.  I personally would like to see it 
mandatory that any such appliance be field adjustable at the POC, ideally in 
both flow and no-flow conditions.  But that would essentially
prescribe either an Elkhart or Giacommini and we can't do that.   But if
we could, we could specify that systems be capable of high pressures and
then set the valves down to a lower one.   In San Diego, our
firefighters carry adjusting rods for those valves in their hose packs and we 
do have a policy here that mandates the use of one or the other
product.   Contrast that with City of San Francisco, where trucks carry
three sets of tips so that fire fighters can effectively use standpipes
from three different eras.   As mentioned previously the One Meridian
fire was NOT an example of PRV failure - they worked perfectly.   The
fire went out of control because of a lack of sprinklers and a complete 
meltdown by building security, but when the FD finally arrived and tried to wet 
it down they were using 100psi tips on valves set for 65psi max
and they only had 15 usable PSI at point of attack.   It is CRITICAL
that the standpipe system be capable of providing pressure across a usable 
range for firefighters responding from a particular agency and we
(industry) have to remember that sometimes decisions are made by purchasing 
agents who outfit hose packs with a particular nozzle and that's that for the 
next however many years.  Then, the question becomes, will the next PA buy new 
equipment with the same performance
parameters?    

Whenever I do a seminar or when I'm pontificating (as now), I always say that 
standpipes should be performance based as a first option.  If a Fire Department 
needs/wants pressures in excess of the NFPA 14 prescriptives, they should 
establish a policy or engineering bulletin and put it out there.  If an FD 
expresses a preference for this pressure or that, industry should conform 
unconditionally and without question; it's their system, not ours or the 
building owner's.  But keep in mind too that there are still a few FD's out 
there using straight streams that allow/require lower pressures: does anyone 
know if Tampa Bay is still using 65psi?

The foregoing is my opinion only and does not necessarily represent the opinion 
or intent of the NFPA 14 Technical Committee on Standpipe and Hose Systems.

Steve Leyton
Protection Design & Consulting
San Diego, CA



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steven 
Scandaliato
Sent: Wednesday, February 19, 2014 11:01 AM
To: [email protected]
Subject: RE: 100 PSI requirement at top of Standpipe

Bingo....the title for NFPA 14 should be changed to "Standard for the 
Installation of Standpipe Systems"....Chapter 1 - Call the guy who is going to 
fight the fire and ask him what he wants".  Chapter 2 - "don't argue with the 
guy who is fighting the fire; rather give him what he is asking for".
Chapter 3 - Do chapter 1 and chapter 2 BEFORE you bid the job.

Peace,

Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to