To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Air Testing CPVC Piping

I think all you guys using 50 psi to test plastic are crazy. I also think that 
guys that pipe shop air in plastic are crazy. That said I know it's done all 
the time without mishap. Puff test for holes. Water test for pressure holding 
ability.

And what the hell is a polar vortex. Sounds like Winter Blast 2014 (which may 
be appropriate for you Easies this year).


On Tue, Feb 25, 2014 at 10:25 AM, Morey, Mike <mo...@bmwc.com> wrote:

> NFPA 13 2010
> A.10.10.2.2.1 might be worth pointing out, specifically:
> When systems having rigid thermoplastic piping such as CPVC are 
> pressure tested, the sprinkler system should be filled with water. The 
> air should be bled from the highest and farthest sprinklers. 
> Compressed air or compressed gas should never be used to test systems 
> with rigid thermoplastic pipe.
>
> I would avoid it if at all possible, and especially a pressure as high 
> as
> 50 psi, you're making a plastic pipe bomb at that pressure.
>
> Mike Morey, CFPS, SET
> Planner Scheduler/Designer
> BMWC Constructors, Inc.
> 1740 W. Michigan St, Indianapolis, IN 46222
> O: 317.651.0596 | C: 317.586.8111
> mo...@bmwc.com | www.bmwc.com
>
> ________________________________________
> From: sprinklerforum-boun...@lists.firesprinkler.org [ 
> sprinklerforum-boun...@lists.firesprinkler.org] on behalf of Richard 
> Mote [rich...@rowesprinkler.com]
> Sent: Tuesday, February 25, 2014 12:46 PM
> To: sprinklerforum@lists.firesprinkler.org
> Subject: Air Testing CPVC Piping
>
> We have an AHJ requiring a 50 psi test on CPVC piping, we think that 
> is excessive, and have always used 20 psi max. I know the best 
> practice is to do a hydrostatic test, but thanks to the polar vortex 
> we are having freezing temperatures and the builder needs to close up 
> his walls. Right now we are looking for chapter and verse as to what 
> the maximum recommended pressure is for an air test. Have looked 
> through 3 different CPVC installation handbooks but the number is not 
> jumping out at me. The TYCO Residential Dry System runs 10 - 15 psi 
> pressure. Note: This is not  a residential dry system we are trying to 
> air test a system so the drywall can go on. When the building gets the 
> heat turned on it will be a wet system.
>
> Richard L. Mote
> Rowe Sprinkler Systems, Inc.
> 7994 Route 522, Suite 1
> PO Box 407
> Middleburg, PA 17842
> P 570-837-7647
> F 570-837-6335
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to