Then you would have to make it right or take it out. If a system is installed, 
it has to be per code, whether it is required or not

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Feb 27, 2014, at 4:46 PM, Steven Cook <[email protected]> wrote:
> 
> Depending on placement of the full height walls, it is possible some of these 
> existing heads could now be positioned as exceeding the maximum distance from 
> walls.....
> 
> Steve 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Todd - 
> Work
> Sent: Thursday, February 27, 2014 4:44 PM
> To: [email protected]
> Subject: Re: Interstitial Space Sprinklers
> 
> However, if the upright sprinklers are still connected and operational, why 
> wold they need to be taken out? If some of the existing heads are removed and 
> the outlets used as drops (without installing new uprights), then all of the 
> uprights in that area should be removed.
> 
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> www.fpdc.com
> 860-535-2080 (ofc)
> 
>> On Feb 27, 2014, at 4:35 PM, Richard Lindner <[email protected]> 
>> wrote:
>> 
>> Based on prior discussions here, this is a cited reference (IFC 2012
>> 901.4.5) if applicable.
>> 
>> "Any device that has the physical appearance of life safety or fire 
>> protection equipment but that does not perform that life safety or 
>> fire protection function shall be prohibited"
>> 
>> 
>>> On Thu, Feb 27, 2014 at 4:23 PM, Steven Cook <[email protected]> wrote:
>>> 
>>> We have a fit-out project of an existing core / shell condition building.
>>> Beam and girder construction, all noncombustible.  Existing 
>>> sprinkler coverage is average 10 x 12 spacing for the open space.  
>>> Accounting for beam and other MEP obstructions as required, etc.  The 
>>> contract drawings are depicting new branch line piping supplying the 
>>> sprinklers at the ACT
>>> ceilings.   Deck at 15 feet, new ceilings range from 8'6" to 10 feet.  They
>>> currently depict the existing upright heads to remain.
>>> 
>>> I believe the existing heads are 165 F, but need to verify.  It's the 
>>> ground floor of a multi-story building (so not at an un-insulated roof).
>>> 
>>> Although the heads are not required, is there a requirement to remove the
>>> existing upright heads?   I thought there was, but didn't locate it.
>>> Pushing to remove them, but want to have back-up when told to "prove" 
>>> they need to come out.
>>> 
>>> Thanks
>>> 
>>> Steve Cook
>>> TG Gallagher
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>> ler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to