Richard hit it with, "Any device that has the physical appearance of life
safety or fire
protection equipment...." This is the key. Unused stuff that isn't life
safety in appearance need not be removed if non-functional, but if life
safety it has to come out or, as Todd said, needs to be in full compliance,
whether required or not. So if it's life safety stuff and not required it
can stay or go as long as it works properly, but if out of compliance it
must be right or it must go.


On Thu, Feb 27, 2014 at 1:56 PM, Todd Williams <[email protected]> wrote:

> Then you would have to make it right or take it out. If a system is
> installed, it has to be per code, whether it is required or not
>
> Todd G Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860-535-2080
> www.fpdc.com
>
>
> > On Feb 27, 2014, at 4:46 PM, Steven Cook <[email protected]> wrote:
> >
> > Depending on placement of the full height walls, it is possible some of
> these existing heads could now be positioned as exceeding the maximum
> distance from walls.....
> >
> > Steve
> >
> > -----Original Message-----
> > From: [email protected] [mailto:
> [email protected]] On Behalf Of Todd - Work
> > Sent: Thursday, February 27, 2014 4:44 PM
> > To: [email protected]
> > Subject: Re: Interstitial Space Sprinklers
> >
> > However, if the upright sprinklers are still connected and operational,
> why wold they need to be taken out? If some of the existing heads are
> removed and the outlets used as drops (without installing new uprights),
> then all of the uprights in that area should be removed.
> >
> > Todd G Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > www.fpdc.com
> > 860-535-2080 (ofc)
> >
> >> On Feb 27, 2014, at 4:35 PM, Richard Lindner <[email protected]>
> wrote:
> >>
> >> Based on prior discussions here, this is a cited reference (IFC 2012
> >> 901.4.5) if applicable.
> >>
> >> "Any device that has the physical appearance of life safety or fire
> >> protection equipment but that does not perform that life safety or
> >> fire protection function shall be prohibited"
> >>
> >>
> >>> On Thu, Feb 27, 2014 at 4:23 PM, Steven Cook <[email protected]>
> wrote:
> >>>
> >>> We have a fit-out project of an existing core / shell condition
> building.
> >>> Beam and girder construction, all noncombustible.  Existing
> >>> sprinkler coverage is average 10 x 12 spacing for the open space.
> >>> Accounting for beam and other MEP obstructions as required, etc.  The
> >>> contract drawings are depicting new branch line piping supplying the
> sprinklers at the ACT
> >>> ceilings.   Deck at 15 feet, new ceilings range from 8'6" to 10 feet.
>  They
> >>> currently depict the existing upright heads to remain.
> >>>
> >>> I believe the existing heads are 165 F, but need to verify.  It's the
> >>> ground floor of a multi-story building (so not at an un-insulated
> roof).
> >>>
> >>> Although the heads are not required, is there a requirement to remove
> the
> >>> existing upright heads?   I thought there was, but didn't locate it.
> >>> Pushing to remove them, but want to have back-up when told to "prove"
> >>> they need to come out.
> >>>
> >>> Thanks
> >>>
> >>> Steve Cook
> >>> TG Gallagher
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>>
> >>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
> >>> ler.org
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> >> er.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to