Thank you Steve. While I sometime disagree with your perspective, on this we 
both agree, and wholeheartedly! I am regularly irritated by our industry 
generated "slang" vernacular. "Heads", "sprigs", "drops", "shotgun risers", and 
"FDC Connections" to name a few, should be systematically expunged from our 
vocabulary, and I will lay down this challenge to the Professionals, Tradesmen, 
Scholars, Authorities, and all other participants of this Forum to do this. 
Mark at Aero

----- Original Message -----
From: Steve Leyton [mailto:[email protected]]
Sent: Thursday, February 27, 2014 11:43 PM
To: [email protected] 
<[email protected]>
Subject: RE: Interstitial Space Sprinklers

Memo To:  Everyone in our industry who is alive and being held to the Earth's 
surface by gravity (as personified by Brad) 

In Re To: "head makers"

In reference to the appliances that discharge water in fire suppression 
systems, let it be known that there is no such thing as a "head" or "head 
maker" or "sprinkler head" in any context, except when referring to or 
describing pressure, both positive and negative.   The term "sprinkler head" - 
which is and has been used for the entirety of recorded history as we know it - 
is not a defined term.  As such, there is no such thing as a "sprinkler head" 
and therefore, no such entity or group of stake-holders as "head makers", lest 
you be referring to fire pumps, plural/inclusive.    We've all done it, said 
it, used it, myself included but there is no such thing as a sprinkler head.

Let's all start referring to them as "sprinklers" or "fire sprinklers" ...

SML


-----Original Message-----
From: [email protected] on behalf of Brad 
Casterline
Sent: Thu 2/27/2014 8:13 PM
To: [email protected]
Subject: Re: Interstitial Space Sprinklers
 
Since it will come down to leaving the uprights alone or replacing them with a 
plug, and the latest technological thinking of the head makers is that they 
should never be re-installed anywhere if they have been tampered with, I would 
leave them, and CALL them plugs ;)

> On Feb 27, 2014, at 9:43 PM, Brad Casterline <[email protected]> wrote:
> 
> An instance of AHJ "taste"?
> 
>> On Feb 27, 2014, at 8:57 PM, Brad Casterline <[email protected]> wrote:
>> 
>> I will take the contrarian side and say although you all are correct I think 
>> it applies to under-designed and in this case if the above compliment was 
>> left it would be over-designed.
>> 
>>> On Feb 27, 2014, at 8:41 PM, "rongreenman ." <[email protected]> wrote:
>>> 
>>> Richard hit it with, "Any device that has the physical appearance of life
>>> safety or fire
>>> protection equipment...." This is the key. Unused stuff that isn't life
>>> safety in appearance need not be removed if non-functional, but if life
>>> safety it has to come out or, as Todd said, needs to be in full compliance,
>>> whether required or not. So if it's life safety stuff and not required it
>>> can stay or go as long as it works properly, but if out of compliance it
>>> must be right or it must go.
>>> 
>>> 
>>>> On Thu, Feb 27, 2014 at 1:56 PM, Todd Williams <[email protected]> wrote:
>>>> 
>>>> Then you would have to make it right or take it out. If a system is
>>>> installed, it has to be per code, whether it is required or not
>>>> 
>>>> Todd G Williams, PE
>>>> Fire Protection Design/Consulting
>>>> Stonington, CT
>>>> 860-535-2080
>>>> www.fpdc.com
>>>> 
>>>> 
>>>>> On Feb 27, 2014, at 4:46 PM, Steven Cook <[email protected]> wrote:
>>>>> 
>>>>> Depending on placement of the full height walls, it is possible some of
>>>> these existing heads could now be positioned as exceeding the maximum
>>>> distance from walls.....
>>>>> 
>>>>> Steve
>>>>> 
>>>>> -----Original Message-----
>>>>> From: [email protected] [mailto:
>>>> [email protected]] On Behalf Of Todd - Work
>>>>> Sent: Thursday, February 27, 2014 4:44 PM
>>>>> To: [email protected]
>>>>> Subject: Re: Interstitial Space Sprinklers
>>>>> 
>>>>> However, if the upright sprinklers are still connected and operational,
>>>> why wold they need to be taken out? If some of the existing heads are
>>>> removed and the outlets used as drops (without installing new uprights),
>>>> then all of the uprights in that area should be removed.
>>>>> 
>>>>> Todd G Williams, PE
>>>>> Fire Protection Design/Consulting
>>>>> Stonington, CT
>>>>> www.fpdc.com
>>>>> 860-535-2080 (ofc)
>>>>> 
>>>>>> On Feb 27, 2014, at 4:35 PM, Richard Lindner <[email protected]>
>>>> wrote:
>>>>>> 
>>>>>> Based on prior discussions here, this is a cited reference (IFC 2012
>>>>>> 901.4.5) if applicable.
>>>>>> 
>>>>>> "Any device that has the physical appearance of life safety or fire
>>>>>> protection equipment but that does not perform that life safety or
>>>>>> fire protection function shall be prohibited"
>>>>>> 
>>>>>> 
>>>>>>> On Thu, Feb 27, 2014 at 4:23 PM, Steven Cook <[email protected]>
>>>> wrote:
>>>>>>> 
>>>>>>> We have a fit-out project of an existing core / shell condition
>>>> building.
>>>>>>> Beam and girder construction, all noncombustible.  Existing
>>>>>>> sprinkler coverage is average 10 x 12 spacing for the open space.
>>>>>>> Accounting for beam and other MEP obstructions as required, etc.  The
>>>>>>> contract drawings are depicting new branch line piping supplying the
>>>> sprinklers at the ACT
>>>>>>> ceilings.   Deck at 15 feet, new ceilings range from 8'6" to 10 feet.
>>>> They
>>>>>>> currently depict the existing upright heads to remain.
>>>>>>> 
>>>>>>> I believe the existing heads are 165 F, but need to verify.  It's the
>>>>>>> ground floor of a multi-story building (so not at an un-insulated
>>>> roof).
>>>>>>> 
>>>>>>> Although the heads are not required, is there a requirement to remove
>>>> the
>>>>>>> existing upright heads?   I thought there was, but didn't locate it.
>>>>>>> Pushing to remove them, but want to have back-up when told to "prove"
>>>>>>> they need to come out.
>>>>>>> 
>>>>>>> Thanks
>>>>>>> 
>>>>>>> Steve Cook
>>>>>>> TG Gallagher
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>> 
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprink
>>>>>>> ler.org
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>> er.org
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> 
>>> 
>>> -- 
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> [email protected]
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis Bacon,
>>> essayist, philosopher, and statesman (1561-1626)
>>> 
>>> A problem well stated is a problem half solved. -Charles F. Kettering,
>>> inventor and engineer (1876-1958)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to