Art,
Thanks for the reply. Table 16.2.1.3.2 states it is for racks "without solid shelves". 13 then goes on to talk about multiple row racks, ESFR's, etc. but I don't see anything about solid shelves. Bill Menster WFM Consulting Inc. ----- Original Message ----- From: "Art Tiroly" <[email protected]> To: [email protected] Sent: Friday, March 14, 2014 2:35:44 PM Subject: RE: Solid Shelf Rack Storage Ceiling Density? See Fig 16.2.1.3.2B. With in-rack sprinklers and adjusting with fig 16.2.1.3.4.1 to 60% of 20 Ft. required. OR Is this miscellaneous stge or a rack warehouse? Art Tiroly ATCO Fire Protection/Tiroly 24400 Highland Rd CLE 44143 216-621-8899 216-570-7030 cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Friday, March 14, 2014 2:03 PM To: [email protected] Subject: Solid Shelf Rack Storage Ceiling Density? Hi, Newbie to the forum here. I have Solid Shelf Rack Storage (not shelf storage), Class 2 commodities, 15' high. 13-16.1.6 indicates rack sprinklers are required at each level, however, I cannot find the density required for the ceiling sprinklers. Can anyone help? Thanks Bill Menster WFM Consulting Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org