Art, 

Thanks for the reply.  Table 16.2.1.3.2 states it is for racks "without solid 
shelves".  13 then goes on to talk about multiple row racks, ESFR's, etc. but I 
don't see anything about solid shelves. 




Bill Menster 
WFM Consulting Inc. 

----- Original Message -----
From: "Art Tiroly" <[email protected]> 
To: [email protected] 
Sent: Friday, March 14, 2014 2:35:44 PM 
Subject: RE: Solid Shelf Rack Storage Ceiling Density? 

See Fig 16.2.1.3.2B. With in-rack sprinklers and adjusting with fig 
16.2.1.3.4.1 to 60% of 20 Ft. required. 
OR Is this miscellaneous stge or a rack warehouse? 


Art Tiroly 
ATCO Fire Protection/Tiroly 
24400 Highland Rd CLE 44143 
216-621-8899 
216-570-7030 cell 



-----Original Message----- 
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected] 
Sent: Friday, March 14, 2014 2:03 PM 
To: [email protected] 
Subject: Solid Shelf Rack Storage Ceiling Density? 




Hi, Newbie to  the forum here. 

   

I have Solid Shelf Rack Storage (not shelf storage), Class 2 commodities, 15' 
high.  13-16.1.6 indicates rack sprinklers are required at each level, however, 
I cannot find the density required for the ceiling sprinklers.  Can anyone 
help? 

   

Thanks 




Bill Menster 
WFM Consulting Inc. 


_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 

_______________________________________________ 
Sprinklerforum mailing list 
[email protected] 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to