Bill,
    There are a couple of questions unanswered.  Among them are:

   Is the storage encapsulated?
   What are the aisle widths?
   What temperature sprinklers are you using at the roof?

Answer those, and then follow Table 16.2.1.3.2 to get your answer. It'll probably lead you to either Figure 16.2.1.3.2(b) or (e), depending on encapsulation. And don't forget to apply Figure 16.2.1.3.4.1.

hope that helps,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, CA 92025-5053
*****Phone 760.745.6181*
Visit our website <http://www.parsleyconsulting.com/> ***
On 3/14/2014 11:03 AM, [email protected] wrote:


Hi, Newbie to  the forum here.

I have Solid Shelf Rack Storage (not shelf storage), Class 2 commodities, 15' 
high.  13-16.1.6 indicates rack sprinklers are required at each level, however, 
I cannot find the density required for the ceiling sprinklers.  Can anyone help?

Thanks




Bill Menster
WFM Consulting Inc.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to