Welcome aboard

In a nutshell you take a ceiling density that is allowed for an open rack while 
addressing all the variable and then add in-racks as required by 16.1.6. That 
includes open rack arrangements with in-racks and a lower ceiling density as 
long as 16.1.6 arrangement meets or exceeds the open rack in-rack arrangement.  
You also get the additional reduction due to in-rack sprinklers exceeding that 
required for open racks dictated by 16.2.1.3.4. This is hidden in section 
16.2.1 (see below).  I tried to have it moved to the 16.1.6 section but I guess 
that makes it too easy so the TC rejected it.  That battle is not over.

16.2.1.3.5 For solid shelf rack storage, Table 16.2.1.3.2 shall be used to 
establish the density/area criteria and in-rack sprinklers shall be installed 
in accordance with 16.1.6.



 

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Mar 14, 2014, at 11:03 AM, [email protected] wrote:

> 
> 
> 
> Hi, Newbie to  the forum here. 
> 
>   
> 
> I have Solid Shelf Rack Storage (not shelf storage), Class 2 commodities, 15' 
> high.  13-16.1.6 indicates rack sprinklers are required at each level, 
> however, I cannot find the density required for the ceiling sprinklers.  Can 
> anyone help? 
> 
>   
> 
> Thanks 
> 
> 
> 
> 
> Bill Menster 
> WFM Consulting Inc. 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to