Tim, also realize that it is going to have to be approved by the local 
authorities. They may have an issue with a hybrid system that the EoR 
specifies. Best to make sure he is on board with that as well. (There is an FM 
in CT that will not accept FM Global design criteria. Consequently, the systems 
ends up needing 2 sets of plans, one the meets NFPA and one for FM Global. Of 
course the same design with different hydraulics). The EoR may spec 
marshmallows, but if the AHJ wants chocolate and graham crackers as well, you 
will need to provide everything. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Mar 15, 2014, at 1:02 PM, "G. Tim Stone" <[email protected]> wrote:
> 
> Ron,
> Thanks, that's what I needed.
> I will write the engineer.
> 
> Regards,
> G. Tim Stone
> 
> G. Tim Stone Consulting, LLC
> NICET Level III Engineering Technician
> Fire Protection Sprinkler Design
> and Consulting Services
> 
>                117 Old Stage Rd. - Essex Jct., VT. 05452
> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>                           [email protected]
> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of
>> rongreenman .
>> Sent: Saturday, March 15, 2014 12:46 PM
>> To: [email protected]
>> Subject: Re: NFPA 13 versus FM Global
>> 
>> Tim,
>> 
>> The EOR can specify marshmallows as fire protection if he wishes. You
> can't
>> but he can. Look at the Fed for example. They want IBC and NFPA 101 and
> the
>> most rigid when there's a conflict. And as their own AHJ they are quite
>> able to dictate thusly. You have the documentation that says this is what
>> he wants. If you're concerned about taking a fall for poor design send him
>> a letter (registered if you're really paranoid with a received return
>> receipt) asking if mix and match is what he really wants. Put a copy, and
>> the receipt, with your paperwork and you've done more than YOUR due
>> diligence, even if he doesn't respond. If you want him to change his mind
>> offer your ideas as an alternative. Maybe it's your birthday and maybe
> not.
>> 
>> 
>>> On Sat, Mar 15, 2014 at 8:23 AM, G. Tim Stone <[email protected]>
>> wrote:
>> 
>>> Forum,
>>> 
>>> 
>>> 
>>> I am working on a warehouse design utilizing ESFR K25.2 Pendent heads.
>>> 
>>> Commodity is Group A expanded, uncartoned plastics, high piled and
> stored
>>> in-racks. Top of storage [17'-0] AFF. Roof peak is [30-0],   1/4 " / 12"
>> roof
>>> pitch.
>>> 
>>> 
>>> 
>>> Question?   Is the following allowed?
>>> 
>>> Since the Commodity falls outside the scope of NFPA 13 the specifying
>>> Fire Protection Engineer of record has specified FM guidelines for
>>> Design criteria, 8-9 Table 6 "Ceiling Level Protection
>>> Guidelines....." for the Commodity using ESFR, K25.2, Ceiling Height
>>> of 30', K25.2, 12 operating heads @ 30PSI. But then He specifies NFPA 13
>> for Spacing and Obstruction
>>> Criteria.   The building is up including Lights and HVAC, (YUUCK) and
>> NFPA
>>> 13 criteria is going to be much easier to work with.
>>> 
>>> 
>>> 
>>> I have always been under the impression we design and install to
>>> either one or the other Standard.
>>> 
>>> 
>>> 
>>> I am crazy, but am I on this one?
>>> 
>>> 
>>> 
>>> Regards,
>>> 
>>> G. Tim Stone
>>> 
>>> 
>>> 
>>> G. Tim Stone Consulting, LLC
>>> 
>>> NICET Level III Engineering Technician
>>> 
>>> Fire Protection Sprinkler Design
>>> 
>>> and Consulting Services
>>> 
>>> 
>>> 
>>>                117 Old Stage Rd. - Essex Jct., VT. 05452
>>> 
>>> CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
>>> 
>>>                            <mailto:[email protected]>
>>> [email protected]
>>> 
>>> 
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>> 
>> 
>> 
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis
> Bacon,
>> essayist, philosopher, and statesman (1561-1626)
>> 
>> A problem well stated is a problem half solved. -Charles F. Kettering,
>> inventor and engineer (1876-1958)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-
>> firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to