So you mean I can't spec aluminum pie pans from the grocery store duct taped to 
the deflectors to trap heat?

Nuts, now I've got to revise another spec...............................   ;)

Craig L. Prahl


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark A. 
Sornsin, P.E.
Sent: Monday, March 24, 2014 11:18 AM
To: [email protected]
Subject: RE: heat collector vs heat director

Where I have seen engineers specify these is in situations where the ceiling is 
considerably higher than the sprinkler - like when a false ceiling is removed 
and they think they can just add 'heat collectors' without otherwise modifying 
the system.  I.e., the sprinklers is several feet below the ceiling, so the 
whole concept of the 'vertical heat director' seems to be a purely academic 
exercise.

Bottom line: heat collectors don't exist and should be shunned at their first 
mention in virtually all settings. 'Heat directors' seem clever, but I fail to 
see a realistic application.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brad 
Casterline
Sent: Monday, March 24, 2014 9:40 AM
To: [email protected]
Subject: heat collector vs heat director

https://www.youtube.com/watch?v=YuuJTxUtPMk&feature=youtu.be



for what it is worth.



16" deflector distance under smooth ceiling.

horizontal heat collector does not work but turning it vertical does.



thanks,



Brad Casterline, NICET IV

Fire Protection Division



FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com



Engineering Solutions for the Built Environment



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to