what Mark said. There are far more failure modes than successful modes for such an arrangement. What about when the fire is offset but parallel to the director? A 1 mm wide director has a significantly reduced capacity. Additionally there is an inherit limit on how far below the ceiling the director will work. At a certain point the buoyancy exceeds the momentum and the downward flow curls back up.
Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Mar 24, 2014, at 8:18 AM, Mark A. Sornsin, P.E. <[email protected]> wrote: > Bottom line: heat collectors don't exist and should be shunned at their first > mention in virtually all settings. 'Heat directors' seem clever, but I fail > to see a realistic application. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org