thanks Mark.

In the model they are 12" square, so the head is 4" below the vertical one.
To me, they are like turning non-obstructed to obstructed at the head only,
but I have only done this one model. I don't know what would happen if we
had a sprinkler 6" below a 16" square 'director'.

Brad 

-----Original Message-----
From: Mark A. Sornsin, P.E. [mailto:[email protected]] 
Sent: Monday, March 24, 2014 10:18 AM
To: [email protected]
Subject: RE: heat collector vs heat director

Where I have seen engineers specify these is in situations where the ceiling
is considerably higher than the sprinkler - like when a false ceiling is
removed and they think they can just add 'heat collectors' without otherwise
modifying the system.  I.e., the sprinklers is several feet below the
ceiling, so the whole concept of the 'vertical heat director' seems to be a
purely academic exercise.

Bottom line: heat collectors don't exist and should be shunned at their
first mention in virtually all settings. 'Heat directors' seem clever, but I
fail to see a realistic application.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Monday, March 24, 2014 9:40 AM
To: [email protected]
Subject: heat collector vs heat director

https://www.youtube.com/watch?v=YuuJTxUtPMk&feature=youtu.be



for what it is worth.



16" deflector distance under smooth ceiling.

horizontal heat collector does not work but turning it vertical does.



thanks,



Brad Casterline, NICET IV

Fire Protection Division



FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com



Engineering Solutions for the Built Environment



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to