Right Roland, thanks--- yesterday I said this: "We would need 2 'baffles', in a "+" shape, to account for the direction the jet is moving when it gets to the head/director". And I am not even going to model more than 6" below a 16" deep director!
I am not selling these things by the way :) Brad -----Original Message----- From: Roland Huggins [mailto:[email protected]] Sent: Monday, March 24, 2014 11:18 AM To: [email protected] Subject: Re: heat collector vs heat director what Mark said. There are far more failure modes than successful modes for such an arrangement. What about when the fire is offset but parallel to the director? A 1 mm wide director has a significantly reduced capacity. Additionally there is an inherit limit on how far below the ceiling the director will work. At a certain point the buoyancy exceeds the momentum and the downward flow curls back up. Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org On Mar 24, 2014, at 8:18 AM, Mark A. Sornsin, P.E. <[email protected]> wrote: > Bottom line: heat collectors don't exist and should be shunned at their first mention in virtually all settings. 'Heat directors' seem clever, but I fail to see a realistic application. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org