I would not focus on the phrase shall be permitted (which taken by itself means 
optional).  I would focus on the portion that states to maintain a horizontal 
distance of 24 inches.  Combine this with Figure 8.6.4.1.3.3 that dictates the 
4 ft separation is a minimum leads to the interpretation that you must be 2 ft 
away on each side and you are allowed to exceed the 36” vertical maximum to 
accomplish it.

Roland

 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Apr 2, 2014, at 11:17 AM, Juan Munguia <[email protected]> wrote:

> My opinion is section 8.6.4.1.3.3 requires a minimum horizontal clearance
> of 24 inches, and therefore allows the deflector to be located at a
> vertical distance greater than 36 inches down from the peak.
> 
> Juan Munguia