Ronald,

This is a very old provision.

The sprinkler spray is clearly disturbed.   

Do you know if this provision is based on any test? 

Dan


www.riskmanage.com
Tel: 972-4-8243337,  972-777-504-011
Fax: 972-4-8243278,
[email protected]

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Wednesday, April 02, 2014 11:26 PM
To: [email protected]
Subject: Re: Steeply pitched roof

I would not focus on the phrase shall be permitted (which taken by itself
means optional).  I would focus on the portion that states to maintain a
horizontal distance of 24 inches.  Combine this with Figure 8.6.4.1.3.3 that
dictates the 4 ft separation is a minimum leads to the interpretation that
you must be 2 ft away on each side and you are allowed to exceed the 36"
vertical maximum to accomplish it.

Roland

 
Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Apr 2, 2014, at 11:17 AM, Juan Munguia <[email protected]> wrote:

> My opinion is section 8.6.4.1.3.3 requires a minimum horizontal 
> clearance of 24 inches, and therefore allows the deflector to be 
> located at a vertical distance greater than 36 inches down from the peak.
> 
> Juan Munguia

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to