It has always been my understanding that any specific requirements in a sub section refer the that section only IE: 8.4.7.2.1 only applies to section 8.4.7 Large Drop Sprinklers. I have had some AHJ's try to apply things like this across the board, but I can usually get a clarification from NFAP to settle the matter.
Richard Mote ET Designer Rowe Sprinkler Systems, Inc. PO Box 407 Middleburg, PA 17842 P- 877-324-ROWE F- 570-937-6335 [email protected] www.rowesprinkler.com -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Vince Sabolik Sent: Friday, May 30, 2014 11:51 AM To: [email protected] Subject: DRY HUMOR from NFPA 8.4.7.2* Galvanized Pipe. 8.4.7.2.1 Where steel pipe is used in preaction and dry pipe systems, piping materials shall be limited to internally galvanized steel. Please straighten me out! This applies to CMSA heads only? Galvanized pipe, where used in a normal dry system must be figured at a C=100?? Thanks! West Tech Fire Protection, Inc. 11351 Pearl Road / Strongsville, Ohio 44136 Phone 440 238-4800 Fax 440 238-4876 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org