Thanks all, especially Ron. I didn't know that the NFPA style manual even
existed!


On 5/30/2014 11:51 AM, Vince Sabolik wrote:

8.4.7.2* Galvanized Pipe.
8.4.7.2.1 Where steel pipe is used in preaction and dry pipe
systems, piping materials shall be limited to internally galvanized
steel.

Please straighten me out! This applies to CMSA heads only?

Galvanized pipe, where used in a normal dry system must be figured at
a C=100??

Thanks!

West Tech Fire Protection, Inc.
11351 Pearl Road   / Strongsville, Ohio   44136
Phone 440 238-4800    Fax 440 238-4876
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org




--