There's provision for sprinklers (and has always been as far back as I go)
for sprinklers in hoods. This is an alternative to CO2, or wet or dry chem,
or any other acceptable protection method for commercial cooking hoods.
Look at 13-10.Figure A.7.10.2. FYI: a hibachi in Japan is a box with
charcoal that's placed under the table (think table at floor level with a
hole under it for your feet and legs) that is then covered with a quilt
that also covers the diners' legs and is used to keep the lower extremities
warm during mealtimes on cold days (think paper walls and no heating system
with snow outside). That morphed into a small table top grill similar to a
Little Smokey but made out of cast iron (original hibachis were wooden
boxes filled with sand). The grills used in a Beni Hana type teppan
(cooking style type like stir fry or teriyaki or tempura)) restaurant  is a
flat grill and so by definition, for our purposes, is a flat grill cooktop
and so falls into the hazard of grease in depth, along with deep fat fryers
and tilting tray skillets. You cannot use sprinklers to protect this type
of cooking surface unless listed for grease in depth. There has not been a
head so listed since the early nineties. You can protect the ductwork and
plenum areas with sprinklers but why would you when the chem system does
that anyways? And if you use a rated and listed for fire protection,
self-cleaning hood you don't need anything except for the surface chem
system.


On Fri, May 30, 2014 at 6:13 AM, Steve Mackinnon <[email protected]>
wrote:

> That's all I saw in that thread too...
>
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Matt Grise
> Sent: Friday, May 30, 2014 9:11 AM
> To: [email protected]
> Subject: RE: Hibachi grills
>
> You might check the mail archive. I recall a lengthy thread on hibachi
> restaurants a while back... although I think it was mostly regarding hazard
> level.
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Steve
> Mackinnon
> Sent: Friday, May 30, 2014 8:07 AM
> To: [email protected]
> Subject: Hibachi grills
>
> Good morning everyone,
>
> I'm working on a small restaurant that will have multiple hibachi
> grills... Somehow my boss got ahold of an old 2000 New York State
> Mechanical code detail showing two upright heads above the fume hood in an
> exhaust plenum. I'm trying to locate a similar detail or requirement in the
> latest edition (2010), has anyone come across this before??
>
> Thanks in advance!!
> Steven
>
>
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering,
inventor and engineer (1876-1958)