Thank you Ron. 
The exhaust duct reduces to a third of its size within the plenum (above the 
grill hood), and the mechanical code is locating the upright heads outside of 
the duct in the cavity created by the reduction. These upright heads will be 
ineffective controlling a fire as they are strangely located. I get the feeling 
that the mechanical code is looking for that last ditch effect to put water on 
an uncontrollable fire... 

Thank you
Steven 

Steven MacKinnon
Fire Protection Division
Hartcorn Plumbing and Heating, Inc.
850 South Second Street
Ronkonkoma, NY 11779
Office 631-580-2300  Fax – 631-580-1090


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Friday, May 30, 2014 2:03 PM
To: [email protected]
Subject: Re: Hibachi grills

There's provision for sprinklers (and has always been as far back as I go) for 
sprinklers in hoods. This is an alternative to CO2, or wet or dry chem, or any 
other acceptable protection method for commercial cooking hoods.
Look at 13-10.Figure A.7.10.2. FYI: a hibachi in Japan is a box with charcoal 
that's placed under the table (think table at floor level with a hole under it 
for your feet and legs) that is then covered with a quilt that also covers the 
diners' legs and is used to keep the lower extremities warm during mealtimes on 
cold days (think paper walls and no heating system with snow outside). That 
morphed into a small table top grill similar to a Little Smokey but made out of 
cast iron (original hibachis were wooden boxes filled with sand). The grills 
used in a Beni Hana type teppan (cooking style type like stir fry or teriyaki 
or tempura)) restaurant  is a flat grill and so by definition, for our 
purposes, is a flat grill cooktop and so falls into the hazard of grease in 
depth, along with deep fat fryers and tilting tray skillets. You cannot use 
sprinklers to protect this type of cooking surface unless listed for grease in 
depth. There has not been a head so listed since the early nineties. You can 
protect the ductwork and plenum areas with sprinklers but why would you when 
the chem system does that anyways? And if you use a rated and listed for fire 
protection, self-cleaning hood you don't need anything except for the surface 
chem system.


On Fri, May 30, 2014 at 6:13 AM, Steve Mackinnon <[email protected]>
wrote:

> That's all I saw in that thread too...
>
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Matt 
> Grise
> Sent: Friday, May 30, 2014 9:11 AM
> To: [email protected]
> Subject: RE: Hibachi grills
>
> You might check the mail archive. I recall a lengthy thread on hibachi 
> restaurants a while back... although I think it was mostly regarding 
> hazard level.
>
> Matt Grisé PE*, LEED AP, NICET II
> Sales Engineer
> Alliance Fire Protection
> 130 w 9th Ave.
> North Kansas City, MO 64116
>
> *Licensed in KS & MO
>
> 913.888.0647 ph
> 913.888.0618 f
> 913.927.0222 cell
> www. AFPsprink.com
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Steve 
> Mackinnon
> Sent: Friday, May 30, 2014 8:07 AM
> To: [email protected]
> Subject: Hibachi grills
>
> Good morning everyone,
>
> I'm working on a small restaurant that will have multiple hibachi 
> grills... Somehow my boss got ahold of an old 2000 New York State 
> Mechanical code detail showing two upright heads above the fume hood 
> in an exhaust plenum. I'm trying to locate a similar detail or 
> requirement in the latest edition (2010), has anyone come across this before??
>
> Thanks in advance!!
> Steven
>
>
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax - 631-580-1090 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________