I overhead a conversation coming from the Code Department where I work one day 
and a major consideration for this topic seemed to be whether the fuel used for 
cooking was in the solid or gaseous phase. Is that spelled out clearly 
anywhere? Is it mostly for the shutting down of the fuel supply part?

> On Jun 1, 2014, at 8:11 PM, "John Drucker - Home" <[email protected]> 
> wrote:
> 
> 2009 IBC/IFC 
> 
> [F] 904.2 Where required. Automatic fire-extinguishing systems installed as 
> an alternative to the required automatic sprinkler systems of Section 903 
> shall be approved by the fire code official. Automatic fire-extinguishing 
> systems shall not be considered alternatives for the purposes of exceptions 
> or reductions allowed by other requirements of this code.
> 
> [F] 904.2.1 Commercial hood and duct systems. Each required commercial 
> kitchen exhaust hood and duct system required by Section 609 of the 
> International Fire Code or Chapter 5 of the International Mechanical Code to 
> have a Type I hood shall be protected with an approved automatic 
> fire-extinguishing system installed in accordance with this
> code.
> 
> [F] 904.11 Commercial cooking systems. The automatic fire-extinguishing 
> system for commercial cooking systems shall be of a type recognized for 
> protection of commercial
> cooking equipment and exhaust systems of the type and arrangement protected.
> 
> Automatic fire-extinguishing systems of the following types shall be 
> installed in accordance with the referenced standard indicated, as follows:
> 
> 1. Carbon dioxide extinguishing systems, NFPA 12.
> 2. Automatic sprinkler systems, NFPA 13.
> 3. Foam-water sprinkler system or foam-water spray systems, NFPA 16.
> 4. Dry-chemical extinguishing systems, NFPA 17.
> 5. Wet-chemical extinguishing systems, NFPA 17A.
> 
> Hope that helps,
> 
> 
> John Drucker, CET
> Assistant Construction Official
> Fire Protection Subcode Official
> Building/Fire/Electrical Inspector
> Borough of Red Bank
> Red Bank, New Jersey
> Email: [email protected]
> Cell/Text: 732-904-6823
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Douglas Hicks
> Sent: Sunday, June 1, 2014 2:25 AM
> To: [email protected]
> Subject: Re: Hibachi grills
> 
> Someplace in the sprinkler code ( or maybe the mechanical code) sprinklers 
> are not required under the hood because there is already a suppression system 
> under the hood.  If sprinklers are in the plenum and the wet chemical is also 
> in the plenum, the sprinklers will dilute the wet chem and the wet chem  will 
> be ineffective.  Hood cleaners get nervous when they find sprinklers in the 
> plenum.  If they hit a head and break the glass bulb, they really get 
> nervous.  They cannot control that much water. A problem I have seen with 
> sprinklers in the hood, is there is no way to test the flow switch to make 
> sure the fuel  supply shuts off.  Of course you could get the inspector to 
> pinch the bulb with pliers.
> 
> Anyway, sounds like you may have an inspector who does not know why UL 300 
> was developed.
> 
> -----Original Message-----
> From: Steve Mackinnon
> Sent: Friday, May 30, 2014 11:49 AM
> To: [email protected]
> Subject: RE: Hibachi grills
> 
> So I'm closer to that first drink of the weekend... nice :)
> 
> Steven MacKinnon
> Fire Protection Division
> Hartcorn Plumbing and Heating, Inc.
> 850 South Second Street
> Ronkonkoma, NY 11779
> Office 631-580-2300  Fax – 631-580-1090
> 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]]
> On Behalf Of rongreenman .
> Sent: Friday, May 30, 2014 2:41 PM
> To: [email protected]
> Subject: Re: Hibachi grills
> 
> Still morning here Steve.
> 
> 
> On Fri, May 30, 2014 at 11:37 AM, Steve Mackinnon <[email protected]>
> wrote:
> 
>> Lol, love the comments on a Friday afternoon, thank you!!!
>> 
>> I think a call to the AHJ would help a lot and see if he'll except 
>> this layout...
>> 
>> Thanks
>> Steven
>> 
>> Steven MacKinnon
>> Fire Protection Division
>> Hartcorn Plumbing and Heating, Inc.
>> 850 South Second Street
>> Ronkonkoma, NY 11779
>> Office 631-580-2300  Fax – 631-580-1090
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum [mailto:
>> [email protected]] On Behalf Of rongreenman .
>> Sent: Friday, May 30, 2014 2:32 PM
>> To: [email protected]
>> Subject: Re: Hibachi grills
>> 
>> The plenum/duct interface is the most dangerous place in the 
>> hood/plenum/duct assembly but it's a Class I Hood System 
>> (combustible/flammable vapors) and so weld sealed along it's entire 
>> length. Mechanical codes require that the duct be insulation wrapped 
>> under certain circumstances (this is a Drucker  for sure, I've only 
>> seen this wrapping in high-rise and within concealed spaces, but I 
>> hesitate to say that's the "WHY" as I've never studied cod on this).
>> This sounds like you are required to either have sprinklers in the 
>> plenum (which would necessitate a penetration--bad juju), or that they 
>> want the area outside the duct/plenum interface protected for the 
>> probably "happened once and we're damned sure not gonna have that 
>> happen again" fire solution. The route of greasy vapors is collected 
>> by the hood and then enters the hood duct system which is a separate 
>> fire area until it encounters some sort of air scrubber or exits the 
>> building (a minimum ten feet from any property line). I love cooking, 
>> eating, cooking history, recipes, cooking fires, both controlled and 
>> not, and cooking/restaurant fire protection. And a good shot of single 
>> malt or a quality mezcal. That's a hint should any of you ever happen 
>> to be where I am and there's a bar close by }:-P
>> 
>> 
>> 
>> On Fri, May 30, 2014 at 11:16 AM, Steve Mackinnon 
>> <[email protected]>
>> wrote:
>> 
>>> Thank you Ron.
>>> The exhaust duct reduces to a third of its size within the plenum 
>>> (above the grill hood), and the mechanical code is locating the 
>>> upright heads outside of the duct in the cavity created by the 
>>> reduction. These upright heads will be ineffective controlling a 
>>> fire as
>> they are strangely located.
>>> I get the feeling that the mechanical code is looking for that last 
>>> ditch effect to put water on an uncontrollable fire...
>>> 
>>> Thank you
>>> Steven
>>> 
>>> Steven MacKinnon
>>> Fire Protection Division
>>> Hartcorn Plumbing and Heating, Inc.
>>> 850 South Second Street
>>> Ronkonkoma, NY 11779
>>> Office 631-580-2300  Fax – 631-580-1090
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum [mailto:
>>> [email protected]] On Behalf Of
>> rongreenman .
>>> Sent: Friday, May 30, 2014 2:03 PM
>>> To: [email protected]
>>> Subject: Re: Hibachi grills
>>> 
>>> There's provision for sprinklers (and has always been as far back as 
>>> I
>>> go) for sprinklers in hoods. This is an alternative to CO2, or wet 
>>> or dry chem, or any other acceptable protection method for 
>>> commercial
>> cooking hoods.
>>> Look at 13-10.Figure A.7.10.2. FYI: a hibachi in Japan is a box with 
>>> charcoal that's placed under the table (think table at floor level 
>>> with a hole under it for your feet and legs) that is then covered 
>>> with a quilt that also covers the diners' legs and is used to keep 
>>> the lower extremities warm during mealtimes on cold days (think 
>>> paper walls and no heating system with snow outside). That morphed 
>>> into a small table top grill similar to a Little Smokey but made out 
>>> of cast iron (original hibachis were wooden boxes filled with sand).
>>> The grills used in a Beni Hana type teppan (cooking style type like 
>>> stir fry or teriyaki or tempura)) restaurant  is a flat grill and so 
>>> by definition, for our purposes, is a flat grill cooktop and so 
>>> falls into the hazard of grease in depth, along with deep fat fryers 
>>> and tilting tray skillets. You cannot use sprinklers to protect this 
>>> type of cooking surface unless listed for grease in depth. There has 
>>> not been a head so listed since the early nineties. You can protect 
>>> the ductwork and plenum areas with sprinklers but why would you when 
>>> the chem system does that anyways? And if you use a rated and listed 
>>> for fire protection, self-cleaning hood you don't need anything 
>>> except for
>> the surface chem system.
>>> 
>>> 
>>> On Fri, May 30, 2014 at 6:13 AM, Steve Mackinnon 
>>> <[email protected]>
>>> wrote:
>>> 
>>>> That's all I saw in that thread too...
>>>> 
>>>> Steven MacKinnon
>>>> Fire Protection Division
>>>> Hartcorn Plumbing and Heating, Inc.
>>>> 850 South Second Street
>>>> Ronkonkoma, NY 11779
>>>> Office 631-580-2300  Fax - 631-580-1090
>>>> 
>>>> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum [mailto:
>>>> [email protected]] On Behalf Of Matt 
>>>> Grise
>>>> Sent: Friday, May 30, 2014 9:11 AM
>>>> To: [email protected]
>>>> Subject: RE: Hibachi grills
>>>> 
>>>> You might check the mail archive. I recall a lengthy thread on 
>>>> hibachi restaurants a while back... although I think it was mostly 
>>>> regarding hazard level.
>>>> 
>>>> Matt Grisé PE*, LEED AP, NICET II
>>>> Sales Engineer
>>>> Alliance Fire Protection
>>>> 130 w 9th Ave.
>>>> North Kansas City, MO 64116
>>>> 
>>>> *Licensed in KS & MO
>>>> 
>>>> 913.888.0647 ph
>>>> 913.888.0618 f
>>>> 913.927.0222 cell
>>>> www. AFPsprink.com
>>>> 
>>>> -----Original Message-----
>>>> From: Sprinklerforum [mailto:
>>>> [email protected]] On Behalf Of Steve 
>>>> Mackinnon
>>>> Sent: Friday, May 30, 2014 8:07 AM
>>>> To: [email protected]
>>>> Subject: Hibachi grills
>>>> 
>>>> Good morning everyone,
>>>> 
>>>> I'm working on a small restaurant that will have multiple hibachi 
>>>> grills... Somehow my boss got ahold of an old 2000 New York State 
>>>> Mechanical code detail showing two upright heads above the fume 
>>>> hood in an exhaust plenum. I'm trying to locate a similar detail 
>>>> or requirement in the latest edition (2010), has anyone come 
>>>> across this
>>> before??
>>>> 
>>>> Thanks in advance!!
>>>> Steven
>>>> 
>>>> 
>>>> Steven MacKinnon
>>>> Fire Protection Division
>>>> Hartcorn Plumbing and Heating, Inc.
>>>> 850 South Second Street
>>>> Ronkonkoma, NY 11779
>>>> Office 631-580-2300  Fax - 631-580-1090 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>> in
>>>> kl
>>>> er.org
>>>> 
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>> in kl er.org _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firespr
>>>> in
>>>> kl
>>>> er.org
>>>> 
>>> 
>>> 
>>> 
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> [email protected]
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis 
>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>> 
>>> A problem well stated is a problem half solved. -Charles F.
>>> Kettering, inventor and engineer (1876-1958) 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl er.org _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
>>> kl
>>> er.org
>>> 
>> 
>> 
>> 
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>> 
>> They are happy men whose natures sort with their vocations. -Francis 
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>> 
>> A problem well stated is a problem half solved. -Charles F. Kettering, 
>> inventor and engineer (1876-1958) 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
>> 
> 
> 
> 
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
> 
> [email protected]
> 
> http://www.bates.ctc.edu/fireprotection/
> 
> 253.680.7346
> 253.576.9700 (cell)
> 
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
> 
> They are happy men whose natures sort with their vocations. -Francis Bacon, 
> essayist, philosopher, and statesman (1561-1626)
> 
> A problem well stated is a problem half solved. -Charles F. Kettering, 
> inventor and engineer (1876-1958) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to