I'd take a common sense approach to this.  If sprinklers were jammed up
against this type of divider, they could be obstructed.  But if storage
height and clearance-to-deflector limits are observed, these don't
present an obstruction.  Are you looking at a mini-storage?   Over the
years, have done many of these throughout the Southwest and the use of
chain link - either full height or just the top 2 feet of framed
partitions - has been the go-to means of allowing us to stretch out
sprinkler spacing and not end up with mean coverage of 50-75 sq. ft. per
sprinkler. 

Steve Leyton

 




-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of IPA
Sent: Tuesday, July 08, 2014 9:16 AM
To: [email protected]
Subject: Chain Link Partitions in Ord Group II

Would chain link 'partitions' (full height to ceiling) be considered an
obstruction for a storage area in an ordinary group 2 occupancy? I'm
having a hard time coming up with anything for this and the closest I
can think of is the privacy curtain requirement for light hazard.