If you go into the definitions section, under Unobstructed Construction, it 
references structural members with openings "at least 70% of the cross section 
area" as being considered unobstructed. This same magical 70% also shows up in 
requirements for mesh in privacy curtains. I think this could be extrapolated 
to include chain link, provided there is over 70% openings in the cross 
sectional area. 

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
www.fpdc.com
860-535-2080 (ofc)

> On Jul 8, 2014, at 12:27 PM, "Steve Leyton" <[email protected]> 
> wrote:
> 
> Got it, we see this in condo communities all the time.  Mini-storage,
> personal tenant storage ... it's all pretty much the same
> compartmentalization mentality.  IMHO the chain link elements are not
> obstructions.
> 
> SL
> 
> 
> 
> 
> 
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of IPA
> Sent: Tuesday, July 08, 2014 9:24 AM
> To: [email protected]
> Subject: Re: Chain Link Partitions in Ord Group II
> 
> This is a large storage area adjacent to a locker room. The storage room
> is divided up into little compartments with chain link 'security mesh'
> while the locker rooms have certain areas that are solid framed up to 2
> ft from the ceiling which is chain link from there on up. I had it
> originally layed out as if they were not obstructions but now that I'm
> starting to finalize everything I'm starting to second guess myself and
> would like to have backup in case plan review questions it.
> 
> 
> 
> On Tue, Jul 8, 2014 at 9:19 AM, Steve Leyton
> <[email protected]>
> wrote:
> 
>> I'd take a common sense approach to this.  If sprinklers were jammed 
>> up against this type of divider, they could be obstructed.  But if 
>> storage height and clearance-to-deflector limits are observed, these
> don't
>> present an obstruction.  Are you looking at a mini-storage?   Over the
>> years, have done many of these throughout the Southwest and the use of
> 
>> chain link - either full height or just the top 2 feet of framed 
>> partitions - has been the go-to means of allowing us to stretch out 
>> sprinkler spacing and not end up with mean coverage of 50-75 sq. ft. 
>> per sprinkler.
>> 
>> Steve Leyton
>> 
>> 
>> 
>> 
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of 
>> IPA
>> Sent: Tuesday, July 08, 2014 9:16 AM
>> To: [email protected]
>> Subject: Chain Link Partitions in Ord Group II
>> 
>> Would chain link 'partitions' (full height to ceiling) be considered 
>> an obstruction for a storage area in an ordinary group 2 occupancy? 
>> I'm having a hard time coming up with anything for this and the 
>> closest I can think of is the privacy curtain requirement for light
> hazard.
>> 
>> Thanks,
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er
>> .org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> 
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler
> .org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to